I've installed a new subpanel and service cable, upgrading it from the 30 amp to 100 amp. I installed a new grounding rod and wire to the new panel. I noticed on the old panel and the main panel, the ground wire is routed away from the power service cable. It seems to run separately and comes through an independent hole in the panel.
Does the ground rod wire need to be separated this way, or can it route into the building through the same hole and come up into the panel through the same panel hole as the power cable?
Additional info per @Greg Hill: The service runs underground from the main house in PVC conduit, using AL 2-2-4-6 mobile home feeder cable. It is protected through the full run and not exposed at any point outside the main house and small guest house we are renovating. The grounding rod is embedded in the earth about 2' from the wall where the subpanel is mounted inside. The copper wire runs up the wall and enters the guest house at the same point the service cable enters, then follows the service cable run up into the panel (approx. 5'). There is another grounding wire that is embedded on the opposite side of the building where the previous subpanel was mounted. I am not attached to this wire for the new panel. The mobile home feeder cable ground is attached to the ground bar in the main house, and to the ground bar in the guest house subpanel. The guest house subpanel is not bonded.