The original compressor-heatpump starting issue is documented at Air-conditioner fan & compressor fails to start. I installed a new capacitor before the technician arrived.

The HVAC technician immediately suspected and removed:

enter image description here

and installed what seems to be a SUPCO SPP6 Relay/Capacitor Hard Start Kit:

enter image description here

I think technician measured the currents and used compressor the LRA / RLA to replace. CERA-MITE device.

enter image description here

Questions

I assume (please challenge if not correct) that the SUPCO SPP6 increases drives the starter such that starting torque is increased. I understand that it somehow reduces the transient starting current, so as to avoid blowing out fuses.

  • Do the devices serve the same function? How are they different (if at all)?
  • Are either of these devices simply supplemental capacitors to augment the charge available to start the compressor?
  • Is does the booster augment the voltage, charge or both to increase the starting torque?
  • How does the SPP6 reduce the starting current, while (I assume) increasing starting torque?
  • What exactly does the compressor RLA=23.5 (Rated Load Amps) indicate?
  • and LRA=105 (Lock Rotor Amps) indicate?
  • How do I know (test) if the compressor is on "final approach" or that this is just a routine parts replacement (heat pump is older: unknown age but in the range of 12-25 years).
1
  • Is the unit working at present? Aug 17 at 18:35
1

I never liked the part shown in the first picture since I never actually understood just how they worked. The Supco SPP6 is a self contained "start kit" which 50 some years ago I could build with a potential relay and a start capacitor. What this SPP6 does is change the phase angle between the start winding and the run winding to near 90 degrees to increase the starting torque and reduce the starting amperage, that 105 LRA figure you quoted. (This is the explanation I was taught in HVAC school in the early 1970's). With the correct size Supco control installed, the compressor should be able to restart almost immediately after a shut down or as we say, a short cycle. Without that Supco device you would have to wait until the head pressure on the compressor would be reduced to that of the compressors inlet which could take several minutes so the compressor could restart with very little resistance. The RLA=23.5 is the expected normal running amperage of the compressor. Amperage higher than that would cause the motor to overheat which could shorten the normal life span of the compressor. When I was still installing A/C and heat pumps I equipped every install with a start kit.

I guess that the term you used of "final approach" to you means that is when the unit fails. These units run until they don't. So, an A/C service tech can't look at a timer or device and say that that unit is about to quit.

Hope this answers some of your questions.