I installed a new GFCI in my garage. It worked when I tested it, but once I screwed it back into the box it tripped and now remains tripped and won't reset. With my GFCI tester plugged into it, when I push the reset button, the lights that indicate it is working correctly come on and the downstream plugged in items work and then it trips after about a second. Any help?
  • Did you separate the neutrals on the load side, downstream?
    – JACK
    Jul 27, 2021 at 19:33
  • Did you peel off the warning tape and attach wires to the "LOAD" terminals? Where do those wires go? I.E. what else loses power when the GFCI trips? Jul 27, 2021 at 22:07
You probably have the earth ground touching the neutral, that will cause it to behave exactly as you describe. Unlikely but it is possible the unit failed. Remove it form the box but do not unwire it and validate that again operates. The other option is something downstream is causing the problem. Unplug everything then one by one plug them back in until you find the problem.
  • This is the second new GFCI so I'm pretty sure I've ruled out a faulty new one. Also, all things unplugged downstream and it still occurs...I removed it from the box and it continues to fail. Jul 27, 2021 at 18:29
  • Disregard, I pulled it back out of the box and it is working. I'll let you know if I push it back in if it works or not. Jul 27, 2021 at 18:38
    @Bradford Oh then probably the bare ground wire touching the "Load" neutral screw. If the box is metal, the ground should be going to the box via a green ground screw on the box. Then, quality GFCI recepts can use their "self-grounding" feature to pick up ground from the metal box, no need to run a ground wire to the GFCI. That lets you push the ground wire down in the back of the box where it'll stay out of trouble. Jul 27, 2021 at 22:09
  • Great you have it. I always place the ground wire on the box then to the device with metal boxes. I do not trust the self pick up ground, if a screw comes loose or something gets in there like paint it can and sometimes does fail. You can always place a piece of sleeving on the ground, appropriate color of course.
    – Gil
    Jul 28, 2021 at 0:25
If you have a tight fit in a box, especially a metal box, combined with wires stripped a drop more than they need to be, you can end up with a short (breaker trip) or a ground fault (GFCI trip). If you put it back in the box and it has the same problem again, take it out, remove and reattach all the wires with special attention paid to making sure that all wire under the screws is stripped but that no wire not under the screws is stripped. And if all else fails, try a wrap of electrical tape (make sure it is real electrical tape, not duct tape or "whatever I have lying around" because anything else may work now but lead to serious problems later) around all receptacle screws as you may have a "just a drop too tight" box.
So, I removed the GFCI, trimmed all of the wires up better so that there was not even one bit of exposed wire and then put a little electrical tape around the ground and over each contact before reinstalling into the box. No issues! Must've been some illicit contact :) thank you so much for the feedback, i was ready to lose my stuff the other day.