I am trying to determine if it's ok to run UF-B from the meter panel and tie in to the NM-B cable underneath the addition and tying them together with wire nuts inside a junction box. (This is to eliminate the underground NM-B to the service panel which is totally within a wet location).
There are two yellow NM cables (14/2 I believe) which are going from the main panel box outside to the underside of the addition built on to the mobile home. I believe one is for the 4 ceiling fans, and the other is for the main room outlets (6 in total).
Can I run 12/2 UF-B from the main panel breaker to somewhere under the addition and tie the UF and Romex together (with wire nuts) within a junction box? The UF-B will be underground and the Romex will be attached to the floor joists before going in to the junction box.
Thank you
  • 4
    Yellow is almost aways 12/2 not 14/2. White may be either depending on age.
    Jul 19, 2021 at 17:10
  • When you say running from main panel box are you referring to the service pedestal or the distribution panel that is part of the mobile home? Jul 20, 2021 at 16:33
  • @isherwood - The original installers ran regular Romex underground from the addition to the Meter panel outside of the house. I am hoping to run UF-B from the meter panel and tie in to the Romex underneath the addition and tying them together with wire nuts inside a junction box.
    – Kurt M
    Jul 20, 2021 at 19:56
  • NoSparksPlease - the service panel with the meter attached.
    – Kurt M
Yes, you can connect UF-B (wet use) cable and NM-B (dry location) cable in a junction box. There's no rule that says you have to continue with UF all the way to a device. As long as the junction box and the NM are in perpetually dry locations it's all fine.
The inverse is also allowed. You can extend a NM-B circuit with UF to serve a wet location outlet, for example.
In my case, I have UF extending a circuit to power a yard shed, in which NM extends the UF. It's a NM-UF-NM sandwich.