I am currently working on my landscaping and I have a concrete pour planned for the front paths.

I'd like to rough in landscape wire for future lighting. What kind of wire should I use, how deep should I burry it?

The lot is ~50' wide and the house is set back maybe 30' from the road. I have various trees and perennial plants planned. Before the concrete path is poured I was thinking I should have home run wires from my line voltage outlet to each area of the landscape where I expect I might want a light. The plan later would then just be to junction or have left enough slack to lay that slack to the final light location.

I am in Canada but I expect the low volt code requirements are the same in the US.

I currently have 4" and 3" sleeves ( just random pieces of PVC/ABS I had lying around ) that are 2' buried below grade at all places where the concrete paths are separating areas of the site. These sleeves run under each piece of pathway. These are to future proof for handling line voltage (120) or potentially adding a line for a car charger in the future - as I could use the sleeves to push through tech cable or conduit.

There are currently trenches for irrigation (1" or 3/4" pvc) for sprinklers that are 8" below grade.

Adding another set of conduit for low voltage lighting could probably use the same trenches as the irrigation. The problem I face having never done low voltage lighting is where to terminate the conduit - since I don't know where the lights will live do I just home run conduit to where I expect to put a transformer and have a home run of conduit from each lighting area to that location? Once the low volt conduit is run to the general lighting area is that enough of a conduit path? Assuming I can feed the low volt wire to the light area some minor trenching afterwards seems reasonable given my lack of a landscape lighting plan. Would I just duct tape the end up of the conduit until a time when I am ready to do the lighting?

Now since the low volt conduit would also be crossing the 8" deep irrigation piping do I go under or above? If 6" is the NEC code for low volt wiring then above?

I've added my irrigation conduit plan. The site is ~50' across the front and the house is ~30' setback. The different colors in the irrigation are different zones.

irrigation plan

4
  • 2
    Are you planning a 12v system? You say low voltage but to a electrician that means something totally different. There limits to the amount of current but not a problem with LED lighting.
    – Ed Beal
    Jun 15, 2021 at 22:32
  • I think 12v is what I was expecting. Jun 15, 2021 at 23:37
  • 1
    Since you have a concrete pour planned, consider if there might be anywhere out there you'd like to have a 120V outlet - concrete cover makes required burial depth for normal voltage conduit quite shallow. Note that low voltage and normal voltage need to be in different conduits, so think about that as a separate item - conduit is inexpensive compared to concrete and labor. So is reinforcing steel, for that matter (most residential pours cheap out on it.)
    – Ecnerwal
    Jun 16, 2021 at 12:12
  • 2
    @ecnerwal, under the concrete can be shallow but when it comes out it has to be 6” below the surface or what the manufacturer allows at least for the NEC requirements.
    – Ed Beal
    Jun 16, 2021 at 14:09

2 Answers 2

30

Conduit

Don't put in wires. You'll guess wrong.

With conduit, you can run multiple wires, change the wires for a larger size, etc. as needed over time. There are limits, but even 1/2" can hold several wires. If you want to play it safe, go up to 3/4" or even 1" and you'll have enough capacity to run power to a shed subpanel or whatever else you might reasonably need in the future.

You may even want to run two separate conduits. One for 120V/240V and another one for low voltage (12V for lighting, network cable, etc.) as they can't go together. Material (a few more sticks of conduit) is cheap, and the extra labor now would be basically zero.

2
  • 2
    Regarding running power to a shed: there are various safety concerns (and thus rules & regs in the electrical code) around running 12v and 120v or even 240v in the same conduit.
    – Eilon
    Jun 16, 2021 at 22:01
  • 7
    Don't put in wires - but do put in a draw cord. Jun 17, 2021 at 10:09
5

Answer In the US and according to the NEC:

Low voltage lighting is limited to 25 amps and 30 volts maximum within these requirements the “low voltage lighting around your yard is required to have a 6” burial depth.

, now the kicker if you purchase a “lighting system” the wire can be on top of the ground in some cases because the manufacturer allows it.

Burial depth from table 300.5

Amperage 411.3

Low voltage 680.33.B

So I would pit in a piece of 1” conduit 7” from the surface this will allow you to even pull in monster #8 landscape lighting if needed for voltage drop.

Even if you know what you want it is a good idea to be able to repair it or upsize in the future.

7
  • 3
    When they were building my house, I sneaked in over the weekend and put in three 1" conduits under the soon to be poured concrete walkway. good move on my part. +1
    – JACK
    Jun 16, 2021 at 1:09
  • 5
    @JACK people like you make contractors' children starve!
    – fraxinus
    Jun 16, 2021 at 13:53
  • 1
    @fraxinus What do you think this site does?? Plus what I did wasn't an offered option...
    – JACK
    Jun 16, 2021 at 14:59
  • 3
    @jack, I have helped folks out long before finding this site. Providing minor help for jobs that just were not worth my time regularly got me the references for the good jobs. It’s that or karma ether way it helped me in the long run and helped those I gave advice to with one exception but that’s another story.
    – Ed Beal
    Jun 16, 2021 at 15:04
  • 6
    Well, I should probably make jokes more recogizable.
    – fraxinus
    Jun 16, 2021 at 15:30