I have 240v over Hot-Hot-Ground which is feeding to a sub-panel for a pool.
Sub-panel will have a 30amp 2-pole breaker for the pool pump and a 15amp breaker for the lights.
I need 120v for the pool lights, but I do not have a neutral.
I found a Square D 50SV1A step-down transformer which will convert the 240v to 120v and provide the needed neutral.
I am going to supply the transformer the 240v using a 2-pole 15amp breaker.
I need to bond the ground lug in the transformer to the ground in the sub-panel. In addition, I also need to bond the neutral leg from the transformer to the ground in the sub-panel.
Is this a correct way to get 120v neutral from 240v?
The answers to other questions suggest this type of fix is expensive, but the transformer is relatively inexpensive compared to opening the walls for new wires.
Can I pull 120v outlets from a 220v box with no neutral?
Case 4: Transformer and subpanel
Edit: (not enough reputation to answer comments)
I didn’t notice that the transformer was only 50w. The lights are about 500w and I’d be driving 2, so that isn’t going to work.
I think the lights are about 30 years old. They are incandescent.