7

I have this outlet with two wires under a single screw on both sides, which I've learned can be resolved through pigtailing. However on the hot side, one of the doubled-up wires is black and the other is yellow. Is it safe to pigtail these two together? I'm not sure what they're for to be honest, nothing is connected to this outlet normally so I'm not sure if it was for something it was previously used for or not. It's a 120 V 20 A outlet. hot neutral

5
  • Yellow in a 120V system? Where do you live? I don't see any countries with color codes that use white as neutral and black and yellow together as line.
    – K H
    May 12 at 2:23
  • 4
    @KH -- yellow for a hot is perfectly fine in North America, it just doesn't show up in "normal" NM cable, that's all May 12 at 2:52
  • @ThreePhaseEel for Canada at the least it should be marked with a band of tape of a 120V color, although I have seen inspectors allow permission for a non-standard wire color for an entire specific system to increase clarity of overall building wiring or when system voltage has been changed, it's unusual.
    – K H
    May 12 at 3:00
  • @KH The NEC generally only requires phase designation by color or tagging when premises branch circuits are fed with more than one nominal voltage system. And then it doesn't specify the colors you have to use except for colors reserved for neutral (grey,white), ground (green,green w/yellow stripe). High leg delta must be orange, but otherwise is often used for 277Y/480v b-leg. May 12 at 13:32
  • I'll say it explicitly: There are two white wires under the bottom screw on the left side. Those should be pig-tailed as well since 2 wires are just as illegal here as they are on the other side.
    – FreeMan
    May 12 at 13:38
16

2 wires under a screw like that is not code compliant. A yellow wire is just like a red, pink, black or blue they can all be hot wires so yes it would be best to pigtail them. If the tab is intact between the 2 screws on that side I would pigtail all 3 together.

If the tab was broken and that was a multi wire branch circuit code would require the neutrals to be pigtailed. So it’s a good idea to do the whites while you’re fixing things.

It really doesn’t matter where the wires go. They could be powering the room lights or another receptacle and until disconnected you may not know

11

You can't put 2 wires under a screw like that, but I gather you knew that.

Yellow is a perfectly legal "hot" color.

You can pigtail them if you like. However, you could also buy a "spec grade" receptacle (the $3 type instead of the 60 cent type). These accept 2 wires under each screw (via a different method) and your 6 wires will fit on there fine.

1

Electrically there's no problem here. From an amateur "common sense" perspective, green/bare is always ground, white is always neutral, and all other colors are hot. The other colors do serve valuable purposes (when used correctly!), but there isn't a crisis here. They all could have been wired up this way for a lot of reasons, but at the top of my list is that a previous homeowner did it and they didn't want to spend more money for wire (choosing to use what they had).

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for? Browse other questions tagged or ask your own question.