I had an electrician install a 220v 40 amp circuit for a new electric range (Avanti DER20P3S) in the basement. The circuit is for a 4 wire (grounded) plug. I have wired the 4 wire plug to the range and removed the bonding strap from neutral to ground. The problem is, the breaker trips immediately when the range is plugged in, due to a ground fault. I have measured continuity with an Ohm Meter from neutral (white) to chassis ground on the range, and there is continuity measuring zero ohms AND the ground strap from Neutral to Chassis has been removed. Is this normal? Is the range incompatible with the GFCI? Keep in mind, the range works normally with a 3 wire connection with the bonding strap installed, as the GFCI can't detect the ground-fault to neutral. Is this an acceptable solution? Note the electrician said a GFCI is code for a basement 220v breaker. Thanks!! Der20p3s wiring diagram
back of range
warning label
ground conn1
ground conn2 ground conn3 correct wiring
  • The 2020 NEC has the requirement for 125-250v receptacles but not all states have adopted the 2020 code. For example in my state the 2020 code was just adopted but they did not adopt the new requirement for 240v receptacles to be GFCI protected. If your state is on the 2017 code the NEC only required 125v 15-20 amp receptacles to provide protected so unless your jurisdiction requires it or one of the 11 states that have adopted it it may not be required. (I ran into this in my state where they are NOT required but the electrician said it was). Other than that I would consult the mfg and report
    Commented Apr 19, 2021 at 18:19
  • The Avanti "DERP 20" range. It seems "DERP" doesn't have the same connotation in your country as it does in the USA. Of course, if it turns out that there's a wiring issue in the oven (as indicated by an answer), maybe it does... :)
    Commented Apr 20, 2021 at 13:30
  • BTW: are you OK with me reporting this issue to the US CPSC? Commented May 2, 2021 at 14:31
  • ...did I lose you? Commented May 8, 2021 at 2:04
  • @ThreePhaseEel Please do! Sorry for the delay. Happy to provide additional details as needed. If you need personal contact information, please message me at styopr1 (at sign) gmail (dot) com and happy to provide
    – Styopr
    Commented May 9, 2021 at 15:27
TL;DR Neutral Not Used, but you may have an actual GROUND FAULT
Most cooktops/ovens/ranges made for use in the USA are combination 120V/240V devices. They typically use 240V for heating (more power!) and 120V for lights/controls/clock. However, there really is no need for 120V - it is a convenience and small (these days, very small) cost savings for the manufacturer, since they can use lights/controls/clocks designed for 120V. Modern lighting (especially LED) can run just as well using 240V supply as 120V. Modern controls are miniature computers, and just like most consumer computers can now handle a range from 100V to 250V, so can the electronics for ovens.
The catch, which seems to have confused Avanti, is that in the USA neutral and ground are almost the same. They are bonded in the main panel and have the same voltage (nominal 120V) relative to each hot wire. Plus, for historical reasons, there are receptacles/wiring methods that combine neutral and ground, even though that is not allowed any more on new circuits (new construction or new/changed installations in existing buildings).
They didn't know what to do about this. They needed to provide a ground - that is a key safety requirement. They thought they needed to use neutral, since every receptacle they connect to in the USA will have a neutral connection. And in some, grandfathered, cases, that neutral and ground will be one and the same.
However, in a new installation, ground and neutral are separate. More importantly, the newest installations now have a GFCI, which will detect an imbalance between the hots & neutral. With a GFCI, if any power comes in on a hot wire and goes out somewhere other than the other hot wire or neutral, the GFCI will trip. The place (except if the power is going through you, which is the real purpose of the GFCI) for that power to go is, naturally, ground.
The first step is to disconnect neutral. The diagram makes it clear that the only place neutral goes is to ground. Which means that if you leave neutral connected to the circuit, neutral and ground are bonded. That is not supposed to be the case. Since neutral is not actually used, the solution to that is to not use neutral - do not connect the neutral wire to the plug. That should have no effect on operation of the range, if everything else is done properly - i.e., the lights/controls/clock will still work since they are powered by 240V and not 120V.
Once that is done, if the GFCI still trips then there is indeed power leaking from one (or both) of the hot wires to ground. Otherwise known as a ground fault. Which is dangerous. Which is a manufacturing defect/warranty repair situation.
Now here is the complicating problem: The instructions clearly state that neutral is to be connected. So not connecting neutral would be OK for testing but not for actual permanent usage, as it violates the manufacturer's instructions, unless you can get the manufacturer to certify that it is OK (e.g., a letter from the engineering department). Which only leaves one other thing to consider, if you have not done so already: the "ground strap". The instructions state not just to unscrew it (which is typical) but to cut the ground strap:
Remove the ground strap from the frame of range and terminal by removing its screw and cutting is as shown.
If you have not done this, doing so may solve the problem. If you have already done so, then it sounds like there truly is a ground fault.
Note that the wiring diagram seems to indicate "Neutral to ground" as part of the normal installation and not as a removable ground strap. But it could be that the diagram is wrong.
  • Comments are not for extended discussion; this conversation has been moved to chat.
    – Michael Karas
    Commented May 1, 2021 at 4:43