Is this wiring scheme a code violation for showing two 14/2 cables controlling a ceiling fan with separate switches for the light and the fan a code violation?

We are remodeling and added ceiling fans and slim Led lights to all four bedrooms. I cut the holes in the ceiling and pulled the 14/2 cable to each hole. There are holes everywhere and the sheetrock taper/texture guy is making it all look great. A licensed Union electrician is installing all the lights and fans and he is making all the wiring connections. However, I am the one who bought the 14/2 cable and ran the cable and the electrician is a commercial electrician working on very large commercial jobs.

The electrician is unable to work for me this weekend so I Googled how to wire a ceiling fan with separate fan and light switches and found multiple posts stating 14/3 cable is the only proper wire to use unless Smurf tube is used. The posts stated 14/2 cable can be used but will not allow separate control of the fan and light.

And, then I found this diagram on HomeDepot.com which shows two separate wires, although the written instructions accompanying the diagram state 14/3.

I just got this reply from the electrician after sending home post from this site titled “Switch leg to light/ceiling fan with two 14/2 cables”

Electrician’s Reply....Good morning....the wiring for the ceiling fans isn’t a code violation..there is no unbalanced load..the white wires are tied together at the ceiling fan box and switch box..a 14/3 wire would be ok also but two 14/2 wires is acceptable..running two 14/2 cables as you did is good✅ there is no unbalanced loads for they share the same circuit..a unbalanced load occurs at the panel for example ..you have two hot wires feeding the panel..when one of the hot is drawing more amps than the other it is unbalanced..panels are calculated for each load served to prevent this..we can check this when I come back..but everything we did is acceptable..have a great weekend!

So, anyway, am I relegated today to buying 14/3 cable, removing the drywall patches before they get taped and textured, disconnecting the 14/2 cable, removing the ceiling fans, pulling 14/3 cable, and waiting until the electrician can return to rewire everything?

https://images.app.goo.gl/WBHozDSgABBJpuDi7

3 Answers 3

2

"the white wires are tied together at the ceiling fan box and switch box" that's a Code violation. That's called paralleling, which NEC 336.20 complexly says "heck no".

Tying all safety grounds together is the right thing to do. Tying all neutrals together is definitely not - it violates 336.20 and 300.3. However, in 99.9% of boxes, tying all neutrals together is correct - you can see where this area is prone to error. Pros who practice entirely in one narrow area tend to drift into bad habits. Particularly in residential, where neutral and ground seem like the same thing since they all go to the same bar in the panel.

You're OK as long as the fan is a fan ONLY, and the lights are separate.

In that case, you keep the neutrals separate in the fan's box. The fan hot & neutral serve only the fan... the light hot & neutral pass through that box and serve only the lights. That's copacetic.

The diagram you found presumes a fan+light combo. And it's wrong.

The diagram you found is for power at the fan/light. Your power comes to the switch, and you want to treat that as a minor difference - no, it's pivotal.

Also, like most diagrams on the Web, it ignores the NEC 2011 code change which requires neutral at the switch. People who are good at drawing diagrams are not good at following Code.

However you have several no-rewire options.

Light is subsidiary to fan (or vice versa)

In this application, a master switch turns on/off everything. When that switch is on, a subsidiary switch will turn on/off only the light. (or only the fan). This master switch cannot be a dimmer, fan speed control or anything other than a plain on/off switch (it can be smart).

Further, subject to AHJ interpretation, if this is the only light in the room, the master must turn on the light. (leaving the fan as subsidiary). Every habitable room must have a light switch which works (for benefit of guests and first responders). That's not allowed to be a puzzle.

Use one /2 cable as the switched-hot to the entire fan/light assembly. So this cable switches on both fan and light. Neutral is present at the switch box, so that is covered.

As far as the second /2, you configure that as a switch loop (always-hot and switched-hot) to control the light. (or the fan if you prefer).

The subordinate switch, which controls only the light, can be dimmable - but it cannot need neutral because it has no access to neutral. It cannot "poach" the neutral from the other cables, because switch loops can't do that and it would be a NEC 300.3 violation. (imbalanced currents in the cable).

Separate neutrals at the light/fan assembly

This requires a light/fan that is specifically wired for this so it significantly constrains your choice of light/fan. The fan in your diagram would not cut the mustard, however, there are fans that would, particularly ones that take retrofit light kits.

Note that each of the /2 cables has a hot and a neutral. The hots will be switched-hots; one for the lamp, one for the fan. I would even re-mark these with colored tape:

Cable 1 is "fan-hot" and "fan-neutral", I'd use red and white.
Cable 2 is "lamp-hot and lamp-neutral", I'd use blue and gray.

The fan hot and neutral go to cable 1. The light hot and neutral go to cable 2. The neutrals ARE NOT tied together in the fan area; they are already tied together at the switch and cannot be tied both places.

Current travels in loops (hence 300.3). All fan current returns on the fan neutral in that same cable. All lamp current returns on the lamp neutral. Thus we comply with 300.3.

You are at liberty to use any type of dimmer, smart switch, motion sensor, speed control or anything you please at the switches.

1
  • Your 336.20 ref comes up empty in my (2017) NEC -- was that a thinko? Commented Mar 27, 2021 at 0:39
0

You diagram is fine except for one caveat.

Current code says there should be a neutral at each switch location (in case a smart switch will ever need to be installed). So you will need to replace the 14/2 with a 14/3 with the white capped off at the switch and black and red being the live and switched live.

The comments about needing a 14/3 will assume that the power supply is at the switch (with the 14/3 carrying 2 switched legs and a neutral) or you have only a single run to the switch pair.

However in the latter case you would need a 14/4 (or a 14/2/2) to get the neutral into the switch as well with. But 2 separate 14/3 will work when the neutrals are not connected on the other side.

6
  • Thank you for your time. The diagram is slightly different in that in my specific situation the power does come in at the switch. My apologies for not stating that initially. So, would you agree I should pull the two separate 14/2 cables and run one 14/3 cable, or two 14/3s?
    – curiousone
    Commented Mar 26, 2021 at 15:23
  • @curiousone the appropriate way to say "thank you" is to click the up arrow buttons next to any and all answers that help you, then, after a day or two, click the check mark next to the one that helped you the most. Take the tour to find out more.
    – FreeMan
    Commented Mar 26, 2021 at 15:58
  • "The diagram is slightly different in that in my specific situation the power does come in at the switch" That's not "slightly"!!! That changes everything. Commented Mar 26, 2021 at 17:28
  • The original question stated the power was at the switch.
    – Ed Beal
    Commented Mar 26, 2021 at 17:44
  • @EdBeal The diagram shows power at the fan. Commented Mar 26, 2021 at 17:59
0

First the circuit for the light is on 1 cable with its neutral and hot. This is ok. Second is the cable for the fan it’s neutral and hot each switch controls a device ok again. no code issue there.

If the mfg states it can be done this way and it is listed by a recognized third party like UL it over rides code per NEC 110.3.B.

Electricians usually use x3 cables as they are cheaper than separate cables.

Both methods work and would be code compliant unless a local code amendment changes the model code. Since there are 2 devices fed from the switch location to have them separate at least 2 hots are needed and a neutral (for power to return on) and a ground