I am looking to replace my old double oven since it has stopped working. It was plugged into the wall via a three prong outlet that is located above the cutout for the ovens in the back of the cabinet above. When reading about installing ovens it appears the standard is for ovens to be hardwired.
Since my house is setup for a 3 prong cord, would I remove the hardwire wiring and then run the 3 prong cord through the conduit and connect it to the oven that way? Is there a way to remove the hardwire wiring? Since the only pictures I can find are just stock photos of the oven it's hard to visualize how this will work.
EDIT: I added a picture of the plug, the old oven was a Whirlpool RBD275PDB and the new oven is a GE JKD3000SNSS. The power requirements for the old oven vs new oven are below:
KW Rating at 208V: New - 5.4, Old - 6.0
KW Rating at 240V: New - 7.2, Old - 8.2
Circuit Amps: New - 30, Old - 40
12
    There are potentially other issues: Does the new oven have the same power requirements as the old oven? Often, newer ovens require more power, in which case you likely need not just a new breaker but new wire from the oven to the breaker. 3-wire (for US) is also generally obsolete, and now may be the time to upgrade it, particularly if you switch to hardwired connection or if you need a larger circuit. Upload pictures of the existing receptacle and the oven breaker in your panel, plus model # of new oven. Mar 22, 2021 at 22:52
    What make and model is your new oven? Also, can you post photos of the inside of the junction box for the oven receptacle? Mar 23, 2021 at 0:03
    3-prongs aren't just obsolete, they're dangerous. A perfectly routine problem with the neutral wire will energize the chassis of the oven. I'd be keenly interested in if there is ground inside the junction box. By the way hardwiring an oven is no big deal, so don't shy away from it merely because it's unfamiliar. Mar 23, 2021 at 0:11
    In my jurisdiction, hardwire is the only legal option for an oven. Mar 23, 2021 at 0:30
    @manassehkatz-Moving2Codidact I added a picture of the receptacle, model information, power requirements for new and old, and not sure where the oven breaker is in my panel since it isn't labeled but all the breakers look the same. Mar 23, 2021 at 13:24
Just an update and answer for anyone that comes across this looking for help. I turned off the breaker to the outlet, removed the outlet cover, removed the outlet hardware so there were just three wires (two hot, one ground). I added a junction box and wired the oven directly. As per the instructions with the oven, neutral and ground went to ground and one hot wire to each of the hot wires. Done and done, super simple.
  • Does this oven require only 208/240 V or does it require 120 V in addition? So does this oven need two line hots and a ground or does it require a neutral as well? This info should be in the installation instructions. Apr 26, 2021 at 15:51
  • @JimStewart It's in the instructions. Only uses the 240 line and if you don't have a neutral line you plug it into the ground. Apr 27, 2021 at 14:05