I am in a situation that is Hot - Switch - Fixture - Fixture - Switch. The Hot is supplied with 14/2, and the remainder romex is 14/3. Both switches will be 3way. I found this drawinng on the internet, but not sure it will work. Do I have to run an additional conductor between the two fixtures? I predict this wiring is not correct. But trying to wrap my head around it, so to speak. enter image description here

Also found this, which I believe will work but requires an additonal conductor. Any thoughts?

enter image description here

5

Don't waste your time. Have a /3 cable bypass the lamps.

This is a rather straightforward problem if you aren't trying to snake the travelers through the bulb sockets. I know you imagine some great cost savings in wire by doing that... forget it.

Besides... running travelers through the bulb sockets is pointless, and takes up a LOT of splice space inside the box. The common octagon box doesn't have the cubic inches to spare for those splices. (you need 2.25 cubic inches per wire entering the box, so passing the travelers through just wastes 9 cubic inches, leaving precious few for the task at hand.

Unless you want to do this with smart switches. Then your "/3 for everything" plan is fine.

The drawings above don't work anyway

The upper drawing, I can't believe it was drawn out in "pro grade" quality, since it's utterly incompetent. (Here's a paid JustAnswer this was told to a customer; comedy follows.) With the left switch down, all bulbs are dead (no power enters the system). With the left switch up, your choices are either L2 lit, or both wired in series. "What were they thinking?"

The lower drawing is a is a hillbilly hack to avoid paying for the proper /4 cable, and violates NEC 300.3.

Again, no reason on earth to drag travelers through octagon boxes. Just have a /3 cable fly from switch to switch, bypassing the lamps. Then make the lamp string a "spur" off ONE of the switch boxes, all with /2. And you're done.

Or use smart switches. You need /3 between the smart switch master and all lamps. (black=always-hot, red=switched-hot, white=neutral).

3
  • So, you're saying it's better to have more connections in the switch jbox than in the fixture jbox? What if we are getting close to the 2 and a quarter per hot in the switch jbox? – Trout Feb 24 at 2:39
  • @Trouf yeah, because switch j-boxes usually have more room in them. The box fill rules I'm talking about are here. – Harper - Reinstate Monica Feb 24 at 2:55