I have a PoN Square D QO 200A rated panel with a 100A main breaker. Model QO154M200P
This panel allows 10 tandem breakers, but as some of you know the older QO double breakers (without the hook) fit anywhere just fine. I used two but I wonder about risks of using more.
Assuming no shared neutrals or mwbc what are the risks of using a few double breakers?
    What vintage of QO panel are we talking about here? (pre-CTL, CTL but not PoN, or PoN?) Feb 22 at 4:01
    Meh, or just stick two 20A circuits on a 40A breaker, which is $10 instead of $20. You barely need breakers anyway, what's the chance of something going wrong? Feb 22 at 4:50
    @ThreePhaseEel it's a PoN panel made in the last 3 years.
    – Matthew
    Feb 22 at 5:05
    Does it even have a CTL rating? CTL was abolished more than 3 years ago. As for understanding the risks, that's the real problem, isn't it? We don't know because UL never tested that. Feb 22 at 5:32
    @Matthew something I've learned from following some of the professional contributors in these forums is that things are done in ways that have been proven safe, and we often don't know "why not" do things other ways. You don't just want to prevent things from exploding in your face the second you turn them on. Sure you want that. But you also want to prevent things from creating quiet but dangerous hazards once in 20 years. And you can't ask "why not" questions in that context ... the only questions are "what has been proven to work?"
    – jay613
    Feb 22 at 16:14
The problem isn't what you think it is
As you have noticed, your panel is not Circuit Total Limiting (CTL) as Square-D has dropped support for CTL from the QO product line. This was done in response to a 2008 NEC (and corresponding UL 67) change that permits panels capable of providing more than 42 circuits. However, unlike Homeline panels which, save for a couple of oddball models, support being fully double-stuffed, QO panels still state a limit on the number of double-stuff (tandem) breakers you can install in them, despite no longer using the CTL QO tandem breakers (QOTxxxx). (They use the old, non-CTL QOxxxx tandem breakers instead.)
This limitation still remains because while your panel can accept 54 breakers, it doesn't have the neutral terminals to support landing 108 circuits. According to the Square-D drawing for your panel, your panel was designed to accept 18 tandem breakers for a maximum of 72 circuits; however, according to the photo you posted in chat and I'm reposting below, you only have 55 neutral terminations available. While this number can be increased using QONK neutral kits, those aren't compatible with "long body" breakers (xFCI, SPD), which limits where in the panel they can go.
As to positioning, that's not too hard to fix. I'd start by swapping the handle-tied pair of doublestuff QO breakers in spaces 17 & 19 with the two-pole 20A breaker in spaces 47 & 49, which takes care of the right side of your (inverted) panel. As to the left side, I would remove the SPD from 38 and 40, then take the double-stuffs out of 6 and 22 and the AFCI out of 8. The AFCI then goes in space 22, the SPD in spaces 6 & 8, and the tandems we removed are reinstalled in spaces 38 & 40. However, due to the lack of CTL support in this panel, and the fact you haven't exceeded the circuit count the panel supports by any stretch of the imagination, I would rank this as a "nice to fix" problem since you don't have the normal risks of neutral terminal shortages and damaged stabs to concern yourself with. (QO CTL worked through a cam that engaged in a slot in the outer backpan mounting rail, so it never had problems with oafs damaging stabs to begin with, even.)
panel photo from DIY.SE chat
  • Thanks for the feedback and great answer. One complication is that 17/19 is actually QO20303020, so moving it will be annoying. The other tandems are more easily changed if I'm inclined. Note that I have plenty of neutrals still because of the AFCI breakers.
    – Matthew
    Feb 23 at 1:30
  • @Matthew -- yeah, in practice the 53-neutral-terminal limit isn't as limiting because you have 2-pole, xFCI, or both breakers roaming around which don't need as many neutral bar screws as spaces Feb 23 at 1:32
    @Matthew yeah, whoever is cutting all your wires short so they can barely reach the breaker, tell them to stop doing that because they're painting you into a corner and leaving you unable to move breakers around. Every hot and neutral should be able to reach any space in the panel. Also, that thing of bunching wires up with cable ties is a very bad idea. Great for Ethernet cables because they don't get warm... but with AC mains cables, this happens. Feb 23 at 7:11
One risk is that if something goes wrong and it catches fire, your insurance company may investigate, discover that you've used breakers in the panel that are not rated for it and decline your claim because it was an illegal installation.
That means that the couple of hundred (maybe couple of thousand?) that you save today by not installing a sub panel to give you loads of extra breaker space could end up costing you hundreds of thousands down the road when you have to replace your house & all your stuff yourself instead of having your insurance company do it for you.
  • Not the OP's situation at all -- his panel is rated for tandem breakers, but not CTL tandem breakers due to PoN QO panels dropping CTL support Feb 23 at 0:30