tl;dr - How can I get water flowing through one of my zones of a baseboard boiler heat system?

I have baseboard boiler heat with 10 zones (5 per boiler). One of the zones (unfortunately, it's our bedroom) is cold. I have vented the air using the 2nd floor vent valve. There was some air initially, but water now comes out.

I disassembled the zone value thinking that was the issue, but when I open it up with the valve fully removed (see picture), water flows initially and then stops. When I reconnect everything and open inlet and outlet valves water seems to flow in the reverse direction (i.e., the outlet pipe is warm and inlet pipe is cool (though not cold).

I've been troubleshooting for a few hours, but I'm stumped. Any suggestions?

enter image description here

Edit: Adding more pictures

Here's the system as I have it now:

enter image description here

Here's a picture of the (removed) valve system. It's a Honeywell 40004850 valve.

enter image description here

Edit #2: the saga continues

All valves for the problematic zone have been checked. I took apart the inlet valve (which was dirty but not clogged). My best guess now is that there is a lot of air in the lines preventing flow. This goes from basement to 2nd floor bedroom. They system's pressure if a bit high (>30 psi according to the pressure gauge), but I'm struggling to get the air out.

I've isolated that zone by closing the other 4 for that boiler hoping that I can get some movement of the air.

10
  • Maybe add in a closeup image of the actual wiring, and a make/model of the zone control valve.
    – FreeMan
    Feb 18, 2021 at 15:40
  • I can certainly do that, but I don't think it's related to that value. No water flows when the value is completely removed (i.e., it's just an open pipe).
    – James Wade
    Feb 18, 2021 at 15:50
  • (Not an HVAC expert, so stupid questions incoming:) This is for the pipe labeled 4? The zone controller is completely removed now (should mount to the copper square? Is it possible that one of the green valves has failed shut?
    – FreeMan
    Feb 18, 2021 at 15:57
  • Yes, pipe 4. Hadn't thought of the green valves failing shut. I'll go investigate.
    – James Wade
    Feb 18, 2021 at 16:00
  • Can you test the electronic control while it's not installed? Can you see it moving to open/close? Can you reinstall it, then force it to open, take it off and see if the valve is opened, then force it closed and see if it actually forces the valve to close? (Again, no expertise, just thinking out loud.)
    – FreeMan
    Feb 18, 2021 at 16:02

1 Answer 1

1

In my personal experience, this is most often caused by a section of the pipe loop in question being frozen. Tends to be aggravated if there's a setback (automatic or manual) at night causing a long "off" time when the weather is particularly cold, or a woodstove causing a long off time for the boiler. Having a "time override" on the circulator/zone can be helpful in that case (to make it run a few minutes every hour, even if there's no call for heat from the thermostat) since the heating pipes are often located in the coldest edges and corners of the house.

Could also happen due to an air blockage causing no flow in that loop while it's particularly cold out.

I managed to thaw one by making sure the boiler inlet was open to refill it from the auto fill valve and wet-vacuuming (a few gallons of) water from the bleeder until I had hot water to the bleeder, which then warmed enough of the pipe to let the ice clog melt and flow resume. After which, more bleeding, since new water always comes with some dissolved air that needs to be bled out.

A different (long-term) solution to loops freezing is to convert the system to polypropylene glycol and water antifreeze mixture. That complicates the fill procedure: you need a pump (not your circulator, which is optimized for a different sort of pumping) rather than just letting water pressure do the trick and you need a reservoir for the antifreeze (and no leaks, but you want no leaks anyway.)

5
  • Looks like it will warm up this weekend, so fingers crossed. I'm leaning toward air being the problem, but I clearly don't know what I'm doing. What I can't make much sense of is the reverse flow. The air is a bit of a challenge to get out with my system. 2nd floor valve throws water out, not air. But, as best as I can tell, the entire inlet line if filled with air.
    – James Wade
    Feb 19, 2021 at 14:09
  • ...which makes me think the (my guess is ice?) blockage is on the inlet line, So backflow is getting water up the oulet line to the bleeder, but if the inlet line is frozen then flow won't happen and that trapped air will still be trapped. If you can apply heat (hairdryer is safer than a torch - people have set their houses on fire melting blockages with a torch) to any exposed parts of the inlet line, that may conduct enough on the copper pipe to partially melt the blockage until some flow can resume and fully melt it, if my past experience and related guess is correct.
    – Ecnerwal
    Feb 19, 2021 at 14:15
  • You should also crank up the temperature in the zones near this zone (either side and below) to aid in potential melting.
    – Ecnerwal
    Feb 19, 2021 at 14:20
  • Thanks for the suggestion. I'll update with either progress or the solution. Do you think that a non-ice clog is unlikely? That's my fear.
    – James Wade
    Feb 19, 2021 at 14:26
  • 1
    Resolved! It was a massive pocket of air. I learned that my pipes are less logically laid out than I thought, but I finally figured out how to release the air.
    – James Wade
    Feb 20, 2021 at 12:44