I recently had frozen pipes in my basement. I took some drywall down to identify the location of the frozen pipes and to apply heat to thaw it. It appears the frozen section is somewhere about halfway between the ceiling and the floor, as when I used a hairdryer directed there it thawed the pipes. The pipes run along an exterior wall which has a layer of insulation and vapour barrier between the wall and the pipe, and then another layer of vapour barrier and insulation between the pipe and the drywall. At first I was upset, as this is a new home and I thought it was poor workmanship; but once I noticed that they actually had 2 layers of insulation and vapour barrier, I began to realize it is most likely they just didn't catch a cold spot which is in actuality making it more of a cooler behind the wall rather than a warm spot. Also, IMO, any insulation between your warm house and piping, especially against an exterior wall, is just going to buffer the warmth from reaching the pipe. But I will see if that is up for debate.

Below I have included 3 pictures of the area. The two pipes running vertical are the hot and cold feeds for the washing machine. The T-connector is a feed for the downstairs shower and also runs behind the wall. The entire column feels cold and I can't tell if that is coming from the corner stud or the top near the joist. I have certainly felt cold air coming from under the joist. The water main line runs into the wall (interior) and comes up through the wall somewhere to the left of the picture along the exterior wall near the ceiling. If having the main run in this location is an issue I can get some closer pictures for you.

In order to do this correctly, I thought of a few options: option one would be to remove the drywall in front of the pipe and install a plastic channel (aesthetics) to run the pipes on the inside (warm) of the wall in addition to insulating the vertical corner stud and gap between the foundation and the joist. Another option would be to just insulate the vertical stud and gap under the joist, repair the vapour barrier and put the pipes back. I would leave the drywall open to make sure that if I didn't insulate all the cold spots I wouldn't have to take the drywall down to thaw the pipes again.

Any other options or comments are much appreciated.

enter image description here

enter image description here

enter image description here

6
  • This is an above grade, outside wall, right? How much insulation (thickness) do you have between the PEX pipes and the outside wall?
    – SteveSh
    Commented Feb 13, 2021 at 16:26
  • And the insulation between the drywall (room) and the pipes is a bad idea in this situation because, as you've pointed out, that just prevents the pipes from being warmed by the air inside the room.
    – SteveSh
    Commented Feb 13, 2021 at 16:27
  • Hi @SteveSh, the pipes you are looking at are below grade below the drywall, and above grade above the drywall (picture 1 shows a good overview). Basically, where the drywall ends is above grade. I find it hard to think that the cold is coming from below grade (please debate this if you think differently), so I could get some minimum expanding foam, insulate all the places above grade, and see if it freezes again tonight. If not, that would be where the cold air was coming from and I might be OK to seal back up. To answer your first question, it looks like 1 sheet of insulation?
    – Matthew
    Commented Feb 13, 2021 at 16:34
  • See my answer below. I agree that the problem is not with the wall that's lower than, say, 36" below grade, depending on where you live. That part of the wall should never go below 45F or 50F.
    – SteveSh
    Commented Feb 13, 2021 at 16:45
  • 1
    After additional digging, I located an old windowsill that had been filled with batt insulation, but inadequatley and the stucco covering on the outside had cracked causing cold air (-45 degrees Celsius) to enter the house, pass the batt and enter the wall cavity. My proposed plan is to have someone spray insulation (as it is a tight space) into the old windowsill, and I will fill in the gaps from the outside once it warms up. That should fix it without having to move the pipe or have them freeze again.
    – Matthew
    Commented Feb 15, 2021 at 14:46

4 Answers 4

1

MOST DEFINITELY POOR QUALITY BUILDING! That said,

#1 - Numero Uno! Remove insulation behind drywall/in between drywall & vertical piping ! This prevents warmth from reaching pipes.

#2 - Option #1 Place moisture resistant [Painted/Wallpapered] greenboard behind the vertical piping IF ABLE. Try to form a niche wall opening to accommodate and incorporate piping into the interior.

#3 - Option #2 Contact Homebuilder (if business shut down, contact 'Registered Agent' that was and still is listed for that business name. Ask City Hall or such other gov't. agcy.). Tell Builder of issue (preferably written, signed, date & time-stamped). Ask for Builder to pay costs/reimburse costs to RECTIFY the issue with no extra burden to you financially or otherwise [you've done your part...you purchased the home]. If no reply within 1 week, call Registered Agent by 12:00 Noon and have 2nd Request Letter Document sent by Messenger in A.M. as back-up documentation & attempt. Still if if no reply then time to file Civil Court - Small Claims Lawsuit wherein a Lawyer can locate the whereabouts of the Registered Agent and have him served! This as you can see is most time-consuming [waiting] and most expensive (filing fee, lawyer retainer fee if not Legal Aid or Student lawyer) option. CHOOSE WISELY BUT KEEP FAMILY INVESTMENT & NEEDS IN MIND foremost. Hope any of this helps!
Per ONE SPIRITUALLY-BLESSED & R.E. Wise Woman!

2

Here's what I would do. If you feel industrious, I would remove that entire cavity's worth of drywall so that the entire wall cavity between the studs is exposed. Then remove all of the batt insulation. Buy a sheet of XPS or polyisocyanurate foam board insulation, cut it to fit, and install it behind the PEX pipes and the outside wall. You want the foam board as thick as will fit behind the pipes. Then finish insulating the cavity with additional foam panels or pieces of batt insulation, but (and this is key here), don't cover the part of the pipes facing the drywall. You want the pipes to receive some warmth from the room.

A somewhat easier approach would be to wrap the pipes with the thickest foam pipe insulation you can find. But, similar to the above approach, remove a section of the pipe insulation that faces the room. You only want to insulate say 3/4 of the pipe against the cold wall, and want the PEX to be heated (through the drywall) by the room.

2
  • Thanks for the comment @SteveSh. Just so I understand correctly, the layout would be exterior wall, insulation, vapour barrier, XPS, varpour barrier then PEX? With this option, like you said, the drywall won't insulate the pipe from the warmth which is what is happening now. I also think it is a good idea to inspect the trim at grade for any air leaks and seal with spray foam or, if the gap permits, regular high R foam insulation.
    – Matthew
    Commented Feb 13, 2021 at 16:48
  • 1
    You only want one vapor barrier, and that is usually on the warm side of the wall.
    – SteveSh
    Commented Feb 13, 2021 at 17:03
0

purchase a length of pipe insulation. It is tube shaped and made of dense foam. There's a split down the middle that allows you to wrap the tube around the pipe.

Also you can install pipe heaters that can keep the pipes warm with electricity.

1
  • I think dealing with the issue would be better than wrapping the pipe in more insulation, but I agree that taking it a step further as you suggested could provide benefit as well. Due to the fact that cold air is coming in the cavity of the wall with 2 layers of insulation which are acting as a cooler, so more insulation around the pipe may not actually fix the issue.
    – Matthew
    Commented Feb 15, 2021 at 14:38
0

It's poor design. Whether the workmanship is poor rather depends on if the workman was following a drawing (poor design) or making it up as they went (poor vernacular design/workmanship.)

In serous cold country, we try to actively avoid plumbing in outside walls (which is very much a design issue of not placing most plumbing items against outside walls), or even on outside walls, but if it's on an outside wall, it's ON the wall, not in it.

As such, I'd recommend the "on the wall" approach to resolving this problem in the least complicated, most effective way.

1
  • Thanks @Ecnerwal, I agree with you that putting the pipe on the outside of the wall (warm side) is the easiest option. However, I was able to find the culprit after some additional investigative digging. There was an old windowsill in that room that had been covered up but with inadequate amounts of insulation and a draft was coming in. It is a tight space, so I think I will get someone to spray the entire windowsill in with insulation and that should prevent any further issues, but also placing the pipe on the other side of the wall probably wouldn't hurt as well.