2

I have a shed that I am using as an office. Since everything that I will need to power (lights, computer, space heater) are already being powered by an extension cord to an outdoor outlet on the house, I won't need a subpanel, and I would like to simply extend the power from an existing 15 amp circuit running along the exterior wall of the house (either from the indoor circuit or outdoor outlet). What do I need to do in order to wire this up to code? I can't run a dedicated circuit because I don't have room in my old service panel in my house.

Update: The distance from house to shed is about 30 feet or less. The extension cord that I'm using is probably only 16 gauge. The space heater that I have been using is a small 500W. But I recently started using an additional 1500W (two heaters, 2000W combined). I assumed that if it was drawing too much power it would have tripped the circuit breaker, but it hasn't. I don't want to install a subpanel or mess with the main service panel due to the difficulty of running a new circuit from the outside of the house to the inside service panel. I don't mind using a larger conduit to make it easier to run new cables in the future if necessary. The main goal right now is to extend an existing circuit as easily as possible while remaining code compliant so that I can get the inspection done, add insulation and cover up the walls.

Here are some photos of my current service panel: service panel diagram

14
  • 1
    Free up two slots in your main panel and install a sub-panel next to it. In the subpanel re-install the breakers and install a new breaker which will feed the subpanel in your shed. Spend a little extra money now to do it right because if you're going to bury wire then at least future-proof it! If not then at least bury a conduit large enough to allow for heavier gauge wire in the future. – MonkeyZeus Jan 19 at 19:58
  • 1
    Distance to shed would be helpful plus the wattage of the space heater. Unless the extension cord is heavy duty, you might already have too much on it, also what else is on the circuit that the outdoor outlet is on. – crip659 Jan 19 at 19:59
  • 4
    Ask another question asking what options you have to update your service panel. Shoot a picture of the panel, its label, and the immediate area around the panel. We can probably help with one option or another (there are many). – Harper - Reinstate Monica Jan 19 at 20:48
  • 1
    Yes -- there are probably better options than feeding the shed from the existing outdoor receptacle circuit, but we'll need much more information about your panel to know what all your options are here – ThreePhaseEel Jan 20 at 1:06
  • 3
    Well some code problems in the panel. That is a rule of 6 or you can not have lore than 6 breakers in the upper section. You have to be able to turn everything off in 6 flips. The good news the bottom section is ok for tandem breakers. You were ok with 500w heater but now with 2000w you should be drawing 16.6 amps and I would bet your receptacle is quite warm if not hot also the wires are probably warm. – Ed Beal Jan 20 at 19:48
3

If you want to tap that circuit, get a box extension that has 1/2” conduit entrance. Most locations will require a “bell box” extension something like a 5400-0 . This brings the existing box out so you can connect conduit to the box and bury it and come up in the office. You will need the conduit from the box down the wall into the ground to burial depth. Depending on the distance and work to bury rigid conduit may be best, only need to bury 6”, if you use pvc 18”, or go with underground feeder / direct burial. If using conduit you will need a thhn/thwn wire type almost all thwn wire is dual rated thwn. With a 15 amp circuit 14 awg wire is needed. There are other ways to tap into circuits but a box extension at an existing location is the easiest. If this is the circuit you are using now you know it will hold for the loads because you are using it now. You will need GFCI protection on the receptacles.

4
  • 3
    Just make sure the conduit is big enough so that when you realize you really do want to put in a subpanel that you won't have to do this all over again. 1/2" is fine for 1 small circuit but limited to 8 AWG = 50 Amp for a subpanel - and that's only if you have metal conduit = no ground wire. Bump up to at least 3/4" and you can go to 6 AWG x 4 wires = 65 Amp with ground = lots of room to spare. – manassehkatz-Moving 2 Codidact Jan 19 at 20:34
  • 1
    I agree putting in larger is my normal suggestion. Once a few months go by then the AC unit and a water cooler, and the next size larger circuit would be common. – Ed Beal Jan 19 at 21:05
  • Thanks for your help! I just added an update which provides more specific information. – Andrew Jan 20 at 18:30
  • 1
    In addition to GFCI protection all receptacles must be tamper resistant as well. I got nailed on my inspection for that. – tnknepp Jan 20 at 19:36
3

DANGER!

First things first, until you get this corrected stop using your 1500W heater! You're seriously overloading your 16 AWG extension cord. That cord is only good for about 870W (source). Very likely the only reason it hasn't melted is that you're using it outside in the cold, so it can shed its excessive heat more easily than normal, but it's only a matter of time before it warms up outside faster than you remember to turn the heater off, and suddenly your grass is on fire.

Trouble in the main panel

Now that you've posted pics of your main panel, there's another issue I want to bring to your attention: you main panel is currently configured in a way that violates both its instructions and the electrical code. Unfortunately, this is not a situation of old work that's grandfathered today, as installing it in that manner was never legal. That means that very likely unpermitted work was done on this panel at some point, and therefore an inspector that sees it has the authority to make you rip it out. This could happen even if they're only coming over to check out your new extension of your existing 15A circuit.

The good news is that the panel itself is perfectly good, despite its age. It's a Murray, which is now owned and supported by Siemens, and breakers for it are widely available, including AFCI, GFCI, DFCI, and other exotic types. There's no need to replace the panel itself.

The trouble comes from how the circuit breakers are arranged. If you look at the diagram in the instructions, you can see that tandem breakers are only allowed in the bottom section, and not in the two upper right positions in the bottom section. Code requires that you follow this labeling, because that's the only configuration the manufacturer & UL safety tested it in. So what you need to do to bring this panel into compliance is to rearrange the breakers such that all of the tandem breakers are in the slots they're allowed to be in.

Unfortunately, doing this won't be as easy as it is on many panels, because this is an old "rule of six" panel that you can't fully deenergize yourself -- you'll need your utility company to pull the meter to kill power to this panel. This is an obsolete design, where the entire top section of the panel is always on, and to fully disconnect your house, you have to flip off every breaker in that top section -- there's no main switch to deenergize everything. The "rule of six" is from older code versions, where you're not allowed to have more than six switches to disconnect all power from a building.

In 2020 code for new installations, it's actually now required to have a single outdoor disconnect. This is so that if your house is on fire, firefighters can quickly turn off all power, so that they can chop through your walls with their big axes to rescue people as needed without fear of getting electrocuted by live wiring inside the wall. When you have your main panel disconnected for breaker rearrangement, strongly consider adding an outdoor disconnect: you'll be compliant with the latest codes, have improved fire safety, and you'll be able to fully deenergize your panel whenever you want. It also opens up Option 3 below.

Now, on to your main question...

Option 1: Run your 15A circuit as planned, and heat with fuel

Unfortunately, heating with electricity takes a lot of power. That's why electric ovens and water heater and such always have dedicated circuits with thick cables running to them. A 1500W heater, like you have, use up the entire capacity of a 15A circuit all by themselves. (*1)

Since you're wanting to heat this space with 2000W, running a single 15A circuit like you propose is insufficient for your heating needs, much less your lights and computers and whatever else is connected to this circuit in your house. Why didn't your breaker trip? When it's only a little overloaded, it takes a while -- the wires in your walls are slowly overheating, and the thermal trip mechanism in the circuit breaker is heating a little faster, such that it'll trip before the wires get too hot. But if it's working properly, it will trip eventually. If it's not, then you could start a fire in your walls.

However, one 15A circuit is plenty to run your lights and computer if you find a different way to heat the space. What I'd recommend is getting a propane or kerosene heater, and using that instead. Or if your home has easily accessible natural gas piping, you can run a gas pipe through the same trench you're using for electrical, and use that instead. This will have the advantage of being cheaper and more efficient to run, too: electric resistive heat is the most expensive kind, since you're basically paying for a power plant to burn some fuel, vent half the heat through their smoke stacks, and send the other half to you as electricity. If you burn the fuel yourself, you can get nearly all of the heat.

Just like your electric heaters, a fuel based heater must be rated for indoor use, and located sufficiently far from anything flammable. Additionally, they'll need a source of combustion air and a place to exhaust the fumes. If your shed is reasonably well ventilated, you can probably get away with the kind that uses the air from the room for combustion (often sold as "ventless"), but some of the bigger and/or the more efficient ones will want you to route both an intake and exhaust pipe outside -- if you want this kind, plan for this before you cover the walls. And in all cases, follow the instructions of the heater to the letter -- that's how they've been tested to run safely. And it would be a good idea to also add a carbon monoxide detector to your shed, to warn you in case anything goes wrong.

If you go this route, for the electrical circuit extension, you can follow Ed Beal's good advice for how to actually extend the circuit. IMO this is the best solution in terms of cost and efficiency.

Option 2: Put a subpanel in your house, and run more power to the shed

Since your main panel is out of spaces, the easiest way to gain more, and therefore gain slots to add a new feed to your shed, is to remove a couple of breakers (or one two-pole) in the main panel, and relocate them to the subpanel. Which one you choose depends in part on where you want the new subpanel -- for example, if you want it outdoors on the wall of your house, you might put it next to your outdoor AC unit, and relocate the AC breaker there. Then you can also run the shed circuit from that location, though the exact options will depend on your house's layout.

Option 3: Split off before the main panel

This option dovetails nicely with correcting the problems in your main panel. With this route, you'd install a panel outdoors, ideally near your electric meter, which will become your new main panel. This panel will contain 2 breakers; one to your current panel (which is now a subpanel), and one to your shed. This arrangement has the advantage that you can kill power to either building independently, from outdoors, which is very helpful for firefighter access. It also solves the problem of being able to deenergize your rule-of-six panel nicely, and brings your installation up to 2020 code. Note that this may require some rearrangement of the grounding within your main panel, and possibly some new ground rods and/or conductors. IMO this is the best long term solution for future expandability.

Consider adding a second conduit

Whichever option you choose, I'd recommend you also add a second conduit to your shed for communications cabling as well, such as ethernet. You can't run most data cables down a power conduit, and adding a second conduit is cheap compared to the cost of digging the trench. Even if you're happy with your wifi performance today, future generations of wifi won't necessarily go through walls as well (that's the tradeoff for higher speeds) and your neighbors might set up access points which interfere with your signal. Adding the option for ethernet now is a very cheap way to future-proof.


(1. Technically, 120V*15A=1800W is the limit of a 15A circuit, but only for things that are intermittent. For something that may be on constantly, like a heater, 1500W is the limit.)

3
  • 1
    I'm not sure what the options are for fuel heating, but I would suggest you add a warning that fuel heaters themselves represent another danger that must be carefully managed. If they are outdoor rated only, they MUST NOT be used indoors; and they MUST NOT be used unattended, or near flammable objects (and a small shed might have few spaces NOT near flammable objects.) Mind you, the latter warnings technically apply to the electric heaters too... – Glenn Willen Jan 22 at 23:12
  • 1
    @GlennWillen, good point, I'll add some additional warnings. Though there are plenty available that are rated for indoor, unattended use. Also, since OP mentions they're wanting to add insulation and cover up the walls, presumably with drywall, the fire danger in the shed shouldn't be worse than anywhere else. – Nate S. Jan 22 at 23:44
  • 1
    @GlennWillen, what I had in mind was something like this: homedepot.com/p/… – Nate S. Jan 22 at 23:57
0

Unfortunately, I don't think you can really do that. You are likely already not code compliant by using a space heater on an extension cord.

But there is hope! Some panels can be expanded by using double breakers (2 circuits from one slot). Or you could add a new Main panel by the meter, making your old main panel a sub-panel and adding as many slots as desired in the new main panel. This would be expensive, but set you up in a better position for the future.

5
  • Deleted the bit about lighting, I probably shouldn't have ventured that far out of my wheelhouse. All the space heaters I've seen say you are not allowed to use them on an extension cord, I assumed that since you must follow instructions that made it a violation. I'll happily delete this answer if it is not good, I'm a bit of a rookie but trying to learn! – izzy Jan 19 at 19:48
  • Yeah it's not the extension cord use, it's overloading and potentially overheating it. I'm pretty sure that all space heaters say not to use them with an extension cord as a condition of their UL listing, and since most of them are 1500W, putting anything else as well on that cord is likely overloading it. – Nate S. Jan 19 at 19:50
  • When did using a extension cord become a code violation? I am not saying the cord to the shed is ok but a properly sized cord is ok. Lighting can be on the same circuit as receptacle or outlet . Two many things wrong to just leave as a comment. By code (NEC 2 circuits are allowed) – Ed Beal Jan 19 at 19:53
  • Think extension cord use on space heaters is a no no because a lot of people have 16 gauge size, only a few people have 14 or better 12 gauge. – crip659 Jan 19 at 20:37
  • Thanks for your help! I just added an update which provides more specific information. – Andrew Jan 20 at 18:31