I'm planning at restructuring my electrical panel. Therefore I want to disconnect the whole panel from the supply wires. The supply wires are 3*400V plus neutral and ground. What is the minimal distance between the supply wires which must be maintained to prevent arcing?

5
  • 3
    Got your will written? Call the power supplier and have them disconnect the supply outside your house. You are heading down a DIY path to killing yourself otherwise. – Ecnerwal Jan 18 at 21:41
  • 1
    Who is your electric utility? – ThreePhaseEel Jan 18 at 21:50
  • I'm not concerned about personal safety. I have protective gear. I have done this before but there is no fuse (afaik) between the electrical panel and the supply wires "upstreams". Don't want to start a fire. – Rubus Jan 18 at 21:55
  • 1
    Cross-site duplicate: electronics.stackexchange.com/questions/300869/… – TylerH Jan 18 at 22:07
  • If wiki can be trusted the distance is extremely small.."For a 7.5 μm gap the arc voltage is 327 V," en.wikipedia.org/wiki/Paschen%27s_law – Rubus Jan 18 at 22:10
8

You need to de-energize the wiring

I realize you're very cocksure, but...

Really, really, you need to de-energize the wiring using the normal methods for doing that in your country.

Absolutely no one on this forum is going to counsel you to do that work "live", even with the much more docile American 120V-to-ground (2 or 3 phases).

Here are the real facts about arc flash.

enter image description here

https://www.youtube.com/watch?v=6hpE5LYj-CY

I recognize this panel as being a common American industrial 480V board. (277V per leg). In America this is considered "industrial-scary" and is treated with grave respect.

However your voltage is only 18% less than this.

You may say "But that's so much more current than I deal with" - nope, when you do stuff like this, the current is limited only by the wires. US power companies guarantee that the wires will limit current to 25,000 amps or 10,000 amps. Even if we assume yours limits to 5000 amps, do you really want to mess with 5000 amps?

This just doesn't work. Pull the meter.

3
  • 3
    One problem with that: having the meter pulled only works in the North American S-base system. most IEC countries eschew socketed meters in favor of a hardwired setup akin to the old A-base meters – ThreePhaseEel Jan 19 at 1:28
  • 2
    @ThreePhaseEel Well they surely have a method for de-energizing it. – Harper - Reinstate Monica Jan 19 at 3:11
  • 2
    Yeah, their arrangements are somewhat different -- in the UK, they'd either send someone out to pull the incomer fuse after flipping the consumer unit main isolator, or have you pull the incomer yourself, not sure what the Swiss do though – ThreePhaseEel Jan 19 at 3:24
4

You're asking about the Dielectric strength of air. Among other things, it depends on the shape of the electrodes (the bare wires) and contaminants in the air (humidity, dust, etc). We can't give a precise answer - but at 400V the distance is quite small. If you can see a gap between the conductors then it's big enough that an arc won't form. Until an unexpected vibration causes the wires to move, close the gap, and strike an arc...