9

If I have NM cable running into a junction box, can I strip the sheath of the NM cable starting inside the junction box and run the conductors without a sheath through conduit that is connected to the junction box?

I understand that the wiring you'd typically use through conduit is THHN or NM (if you want to use the conduit solely as protection). But I'd like to be able to take this incoming NM cable and have it's conductors only continue on through conduit along with some other THHN that's coming from another source.

The individual conductors of the NM cable while not labeled can still be traced back to where the sheathing ends, so technically the conductors are still identifiable as to what they are.

If need be, I could splice the NM conductors to THHN wire in the junction box, but I don't see a reason to add a splice where I don't think it's needed.

My reasoning for why I think this should be OK is that if you terminate NM cable in a panel, you typically have a foot or so of the conductors without the sheath and there's nothing identifying those other than tracing it back to the sheath it came from.

3

2 Answers 2

26

The wires in NM aren't labeled for use outside the cable jacket, and may not be the correct type for use in conduit to begin with

First off, the wires inside a NM cable are not marked or labeled at all, which automatically makes them unsuitable for use in a conduit wiring method, as NEC 310.120 requires conductor insulation to be marked/labeled with the correct insulation type letters, the rated voltage, the wire gauge, and the manufacturer.

Furthermore, the wires in NM are not required to meet any of the type standards in Table 310.104! In fact, while UL 719 section 4.4.1 permits the use of THHN type insulation on wires in NM cables, it also permits the insulation on said wires to meet the standards for type TW wire. It even allows cablemakers to use an insulation material that's not PVC at all, provided it's electrically and mechanically comparable to type THHN insulation and meets the aging requirements set out in UL 1581 Table 50.144.

As a result, you have to treat the individual wires in NM as if they were "mystery meat"; once they have departed the cable jacket, they can only live within a single box, either as wires emerging from a cable that enters the box or "shucked" from their jacket for use as pigtails or jumpers that never leave the confines of said box.

2
  • 4
    Thanks so much for the answer, I really appreciate it! While it's not what I wanted to hear, you lay it out all very clearly. I'm all for following the rules/code it's just that sometimes there seems to be some wiggle room or room for interpretation but I get it. I'll make a splice in the junction box to continue on with THHN through the conduit. I think it was my hesitation to add what I thought was an unnecessary splice, but that's irrelevant since it wouldn't be to code without one.
    – Pink John
    Jan 13, 2021 at 4:01
  • 2
    An additional consideration is that when the shucked NM cables reach the next junction box, they are now unlabeled and unknown. The next guy to look at that box (possibly an inspector) will have no idea what he's looking at and whether it's suitable for purpose.
    – FreeMan
    Jan 13, 2021 at 14:08
9

Or... just run the jacketed cable through the conduit

It is permissible to run the entire, jacketed NM-B cable through the conduit.

The restriction is that it takes a mighty bite out of conduit fill, because the NM-B cable must be treated the same as a round conductor of the wide dimension. This is particularly punishing when there are 2 "wires" (i.e. two NM-B cables) because 2 "wires" are allowed only 30% conduit fill. However, with 3 or more "wires" you are up to a more manageable 40% fill, and this can work at conduit of sane (albeit larger) size.

Also, in some cases, you can gain cross section by switching from /2 NM to /3 NM. That is because some /3 NM cable is made in a round-ish rather than flattish cross section.

4
  • Not, however, in a wet location, as I found myself discussing with my local inspector a few weeks ago.
    – bmargulies
    Jan 14, 2021 at 1:59
  • @bmargulies -- you could run UF thru conduit in a wet location, but there's really no call to Jan 14, 2021 at 2:10
  • And you'd pay for it dearly in needed conduit diameter. UF is very flat and you pay a hefty price for it in conduit fill, due to needing to treat it like a round wire of the wide dimension. Jan 14, 2021 at 18:14
  • My concern is that a reader might make the mistake I made and then have to do the rework I did. Of course, the general point is that running NM through conduit is wasteful, but you might want to edit the answer to add a note about UF and/or wet.
    – bmargulies
    Jan 16, 2021 at 16:15

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge that you have read and understand our privacy policy and code of conduct.

Not the answer you're looking for? Browse other questions tagged or ask your own question.