I'm finishing up the rough in wiring for a kitchen remodel, but I have a situation where I can't run cables through studs for a light switch because there is no wall cavity. I decided to run it strait up against the wall into the attic space through conduit. Its a short 5' run of conduit and just 90 degree stubs out into the attic then connects with the kitchen lighting circuit.
I ended up just stripping the romex back instead of using THHN because I needed the attic portion of the run to be sleeved (I'm aware of the lack of conductor labeling violation here, its just what I ended up doing in my own kitchen). The conduit does NOT connect back to the panel. Is having a bare ground inside conduit going to be an issue? Is this any different from having a ground connected to a metal box?
Any info would be much appreciated, thanks!
  • And I think the "right" way to do this would be a junction box at the top of the conduit, THHN through the conduit, NM connected to the THHN in that junction box and conduit itself as ground. Jan 12, 2021 at 3:55
    We often see people intentionally violate Code, saying "but that's OK, because the purpose of the rule is X". And they are wrong; there are several reasons, but they only looked at the one most convenient to their plan-to-violate. Another reason is the individual wire insulation of Romex isn't anywhere as near as tough as THHN. That said, there's nothing wrong with using a stick of conduit as a damage shield for Romex in its sheath. Jan 12, 2021 at 7:50
  • "It's just my own kitchen" - until you sell it
    – user253751
    Jan 13, 2021 at 21:19