BLUF: need help with what to do with a red wire from the panel.

I'm replacing a bedroom switch with a Kasa smart switch. The old switch didn't control anything (previous owner must have removed the overhead fixture), but I'm looking to connect the new switch prior to installing the fixture.

However I'm seeing that there is a black, red, white and ground wire coming from the wall. Both the red and black are hot. If it helps, this is connected to a tandem breaker.

What should I do with this red wire?

I don't quite understand its purpose here.

Here is a photo for reference (capped for safety):

enter image description here

1
3

I brightened the picture in Photoshop and confirmed there is only one /3 cable coming into this box. That makes it 1 of 3 possibilities.

  • The far "spur/loop" end of a 3-way switch complex.
  • A modern "switch loop" which brings Always-hot, Switched-hot and Neutral (for smart switches).
  • The ceiling box is fan-rated with an obsolete "switch loop", but with an extra wire for separate control of light and fan.

In the last 2 cases, the cables in the wall are the same; you get to decide which of the two it will be, by how you wire it in the ceiling.

This much for sure, we have to see the wiring up in the lamp box to know any more. There is definitely at least one more cable up there. We need to see how they are interconnected, and whether the box has a "Fan Rated" marking.

P.S. Make sure your smart switch has a UL, CSA or ETL listing. We see a LOT of cheap junk flooding the flea-markety mail order channels like eBay, Banggood, DealExtreme and unfortunately Amazon has opened their site to the eBay gang. The junk even ships with Prime because they opened their warehouses too.

Edit:

Given that there is apparently no existing ceiling box, it is most likely a switched receptacle. If there is no ceiling light the only other way to meet Code is a switched receptacle. That greatly increases the likelihood of the second possibility.

Often, rooms are wired with red-white-black circling the room. Black is always-hot, red is switched-hot and white is neutral. Most receptacles are punched down to black and white (always hot). The switched receptacle is punched down to red and white. It was uncommon to extend the /3 all the way to the switch until 2011, but hey, OK :)

Often, such an installation will use a "split" receptacle (tab broken off on the hot side) to allow each socket's hot to be fed from a different wire. One socket gets red (switched) and the other gets black (unswitched).

This would also jibe with the observation that red and black are both hot. Very often, a dumb novice comes along who is changing receptacles for aesthetic reasons. They don't even know tabs are a thing. So they don't look for broken tabs, and they don't break the tab off on the new recep. This has the effect of shorting black and red, making the switch ineffective. The switch stops working, they shrug their shoulders and resign themselves to switching lights off at the floor lamp.

So my working theory is you inherited the above situation. You'll need to open up the receptacle boxes in the room and see what you can see. It may simply be a matter of snapping off the right tab.

15
  • I got the TP-Link Kasa smart switch, I've had good experiences with their other smart products and they're fairly well known. As far as your comments: so you're saying this 14/3 is coming from the ceiling box? Side comment: in other units in my HOA, I believe they have fans in the bedrooms. it's possible they closed up the ceiling but I haven't had a chance to cut into it yet and figure out where the box might be. Dec 30 '20 at 21:22
  • @JonathanNg Well, the box won't be buried - that's illegal. You're not allowed to bury boxes. I get where you feel like "I picked a well-reviewed product and I like it" - nobody's attacking your consumer skills here. The only thing that matters is whether the product is certified by a recognized testing lab. As for those reviews, just type the word "brushing" into Google... Dec 30 '20 at 22:07
  • totally get that, I was just saying I picked a company I know, and as far as I can tell the product is certified. re: burying boxes - there's a chance that happened, which I know is a total code violation, but I can't say for sure what the previous owner did. in my testing, the switch does not control any receptacle in the room. any tips on how to trace where the 14/3 is going? barring ripping my walls down Dec 30 '20 at 22:20
  • 1
    also wanted to add: when I opened it initially, the red and black wires were connected to the switch, but the neutral was capped off on its own. not sure what that means wrt everything we've discussed so far Dec 31 '20 at 1:58
  • 1
    @JonathanNg Interesting. That would suggest a "modern switch loop" with always-hot, switched-hot and neutral(white). That would be good news indeed. If indeed it was a switched socket, it's possible "the last owner" disliked this, and went into the receptacle box and jumpered it to be unswitched. That's a Code violation. It's also possible it had a split recep, and someone changed the recep for unrelated reasons (e.g. aesthetics) and did not realise they needed to break off the tab. That would unsplit it, shorting red and black, making both always-hot. Dec 31 '20 at 3:44