0

I need to add a sub panel to my main panel since it is full. What I was looking to do is put the sub panel (100 amp) beside the main panel (200 amp) then add a 100 amp breaker to the main panel to feed the sub panel.

I'm going to use 6-3 cable for this and hook wires to breaker and then to the main lugs on sub panel. Then I'm going to use a 50 amp breaker in the sub panel to run 8-3 cable to my shed's 50 amp Sub Panel and hook the wires to the main lugs. Then I'm going to use 12-2 cable to feed my lights (15 amp breaker) and 12-2 cable to feed my outlets (20 amp breaker).

Does this all make sense or am I missing something?

6
  • 3
    Can you post photos of the situation around your main panel please, as well as photos of the labeling on the door of your main panel? I'm concerned you may be setting yourself up for unnecessary work later by buying too small of a subpanel... – ThreePhaseEel Dec 27 '20 at 3:25
  • Pictures and make/model of all the panels you have and/or are considering buying. You'll get loads of great advice! – FreeMan Dec 27 '20 at 13:12
  • this is the panel I was going to get, lowes.com/pd/… – Jimmy Dec 27 '20 at 14:55
  • Please add new information to your question post, Jimmy, not down here. – isherwood Dec 27 '20 at 17:49
  • @Jimmy -- can you post more information about your existing setup please? Photos would help tremendously... – ThreePhaseEel Dec 27 '20 at 17:55
3

You are severely under-sizing your cables/wires. Depending upon cable, independent conductors in conduit, over the air, etc. considerations.

For a starter your 100 amp feed to the first sub-panel should be 1 gauge copper, or 2 gauge if THHN/THWN. The feed to the 50 amp sub-panel should at least be 6 gauge.

In your shed, 14/2 is fine on 15 amp breakers for lighting. Easier to work with than 12-2.

On both your planned sub-panels, you'll need to float the neutral (isolate from ground) and have 4-wire (2 hots, neutral and ground) to them. In the separate outbuilding (shed) you'll need to also float the neutral and install ground rods and connect them to the grounding bus bar in the sub-panel. You don't need to do this in a sub-panel in the same structure as the main panel, but you still need to isolate the grounds from the neutral.

Ampacity chart search results

In response to the comments:

It doesn't sound like you've done much load planning. What are you planning on running in the shed, as well as on the sub-panel? I would power the shed's sub-panel from the main panel, even if that means moving a couple more circuits to the sub-panel. Also, 6 ga aluminum wire is considerably less expensive than 8 ga copper. Depending upon how long the run to the shed is, you might want to consider that. And yes, 40 amps on 8 ga copper or 6 ga aluminum is fine. To connect the 100 amp sub, I'd go with a short length of conduit and individual wires. Depending upon your current configuration (in wall or surface mounted), you may need to "assemble as you go" because it would be difficult or impossible to install the conduit later.

You don't need to "buy 4 wires", buy 1 length of 1 ga copper, 3 times the length you need and cut it as you install it. Code tape (wrap) the neutral with white tape. A 6 ga green neutral is fine for ground. Alternatively, I THINK if you ran metal (EMT or rigid) between the main and sub, that would serve as the ground connection. (not sure!)

Also, others may chime in here, but panels are pretty inexpensive compared to the work involved in have to swap them out later if too small, so go big!

Lastly, and please don't take offense to this, but you are asking some pretty basic questions and initially made a pretty bad and dangerous proposal. Electricity is pretty dangerous if not handled properly. If you still want to DIY, it would be a good idea to find a buddy that knows electrical well or even hire an electrician to check your work or get his advice before work is started.

I'm not a licensed electrican, but know quite a bit about it and the code and have done a lot of wiring. Even so, when I wired my son's new house, I paid a licensed electrician to do a "pre-inspection" in case I missed something. And he did find a few things that would have been called out in an inspection.

Hope this helps. There is no honor lost in getting help / advice from pros. In your case, you might need to do that locally.

5
  • 1
    One more thing. Your shed will require a master cut-off switch in the shed. Easiest way is to use a master breaker in the sub instead of a main-lugs sub. The breaker can be a greater amperage than the feeding breaker as the latter will protect the wires. – DoxyLover Dec 27 '20 at 5:24
  • Ok, I will use 1 gauge copper and run it through conduit from the main panel to the sub panel or would it be easier to use 1 cable that has all 4 wires in it then no conduit? if using single wire then i will need to buy 4 wires (2 hot, neutral and ground) and I can run them together through the conduit ? would it be ok to use a 40 amp breaker in the sub panel from the house and a 40 amp breaker in the shed using 8 gauge wire? – Jimmy Dec 27 '20 at 15:23
  • Please see edits to my answer for info. – George Anderson Dec 27 '20 at 17:45
  • 2
    @Jimmy Please follow Harper's Rule: Buy the wire LAST. Like 30 minutes before you install it. Rest assured you are not done learning stuff, and as you learn more, you'll learn more about which wire to use. – Harper - Reinstate Monica Dec 27 '20 at 18:50
  • Thanks everyone, yes I am new to this and probably will end up hiring an electrician but was trying to get an good idea what was involved, 2 of the estimates I got both said they would run 8-3 wire, to save a few bucks I did that myself, it was about 200 feet long and I already ran the wire through my block wall to my main panel so all I need is the wire hooked up to a sub panel from main panel and to the sub panel in the shed, still would cost me $600 for them to do that, that is why I'm asking all the questions to see if I could do this myself, but I guess $600 is a safe way to go. – Jimmy Dec 27 '20 at 19:52
1

I agree, you are undersizing the wires, and dramatically undersizing (cheating yourself out of) panel spaces.

Spaces, spaces, spaces!!!

I certainly don't need to tell you how frustrating it is to be out of panel spaces, since it just happened to you. We run into this every week - someone painted into a corner because the last guy just needed to chintz out. Gosh, I hope they really enjoyed the latté they bought with the savings on shorting you panel spaces!

Panel spaces are cheap! Regrets are expensive. Because of this, we have a saying: Go BIG or go home.

It's a trivial amount of money compared to total project cost, and it guarantees you never have that problem again. EVER.

So think more like a 30-space panel. Seriously. You'll never be back here going "I ran out of spaces again".

Also, double-stuff breakers are all but outlawed today, so you can't rely on "2 breakers per space" like you used to - that "circuits" number on most panels is bull-oney.

Remember to select a panel that provides accessory ground bars with the panel, otherwise you'll have to buy them. These are common "main lug" panels. You must separate neutral and ground in the subpanel.

Connect panels with conduit

Believe me, you'll thank me later for this...

Anytime you mount panels right next to each other, always connect them with several pieces of very short conduit, including a large one. Wherever you can find that the knockouts line up. Go big as you can. You can make these out of

  • Rigid offset conduit nipples (if the panels set that close)
  • plain Rigid conduit nipples with 4 conduit nuts
  • short lengths of EMT conduit with connectors on each end
  • PVC conduit... but then, you have to run a ground wire.
  • Flex is OK, but not a valid ground path
  • Preferably under 2' long (helps a lot)

Metal conduit provides the ground path, so you don't need a ground wire.

Now, this allows you to easily move circuits from one panel to the other. You simply use wire-nuts to extend all the wires except safety ground into the other panel. Including neutral. You can leave safety ground in the original panel, but you must extend neutral because AC power. The several conduit pipes make this very easy! Just go to the nearest one and pop the wires through.

You can use an NM cable with jacket if you really want to, but the most correct thing to use is THHN black and white wires.

As for the 3 main wires (hot-hot-neutral), those can be individual THHN wires and simply come through the big pipe. Bring all 3 through the same pipe. (Safety ground can use a different pipe if you need to wire it).

Wire sizes: 100A feeder

Now, you're off the rails quite a lot on wire sizes. Whatever website or personality you got that from, fire them :)

Here's how we actually determine your wire size needed:

enter image description here

I know that's a busy chart. Firstoff, can't use 90C at all, that's for industrial. At 100A or larger, everything gets to use the 75C column. So that's easy: our only remaining choice is copper or aluminum.

Forget the bad vibes you heard about aluminum, those only ever applied to small branch circuits (15-30 amps) - for feeder, aluminum has always been a good choice. Also, the panel lugs are aluminum because Al lugs play nice with both Cu and Al wire... so if you think copper avoids a dissimilar metal problem, wrong :)

"It's only 4 feet" - sure, I get that logic, but I want you spending extra money on more panel spaces, not copper. Novices who insist on copper wire and then get a tiny panel are a trope around here lol.

So #1 aluminum or #3 copper for your 100A feeder. Easy peasy. I would use three THHN individual wires, and white tape to mark the neutral. Nobody cares if the hots are black+red, but you can mark one of them red if you really want to.

Wire size: 50A Shed feeder

Since we're below 100A, some cables are only good for 60C. That includes NM/Romex cable (which you can't use outside, underground or in outdoor conduit) and UF-B cable (the gray stuff). So this makes the chart a little more complicated.

enter image description here

So you can see where this makes UF cable kinda suck because you must use a larger wire size. (#6 Cu or #4 Al). It also needs to be trenched 25" (for 24" of cover on top).

There are other direct-burial types that allow 75C running, but they generally start at #6 size. So #6 aluminum would probably be the most economical choice there.

PVC conduit is easier, only 19" depth (18" of cover), and then, cheaper wires. (#8 Cu or #6 Al).

Rigid conduit is the easiest to trench, only needing 6" of cover. You can trench it with a garden trowel and don't have to call 311 for a site survey... but it's VERY expensive. So trade off the cost of Rigid conduit vs cost of renting a trencher + risk of slicing through other utilities.

Rigid serves as the ground wire, so you can get your project done with 3 wires and smaller pipe.

Note that if you use individual wires, and neutral is #6 or smaller, you must use native white wire - you can't use black and mark it with white tape.

Due to a separate rule, for <=60A feeder, ground must be #10 copper or #8 aluminum. Again if it is #6 or smaller, it must be natively green or bare - no phase tape allowed. Bare aluminum is not allowed.

3
  • You left out the recommendation to have the conduit to the shed also should follow the go big or go home rule :) – whatsisname Dec 27 '20 at 23:49
  • Wow, that sure explains a lot, with all the great comments it sure makes things to seem easier, maybe I can give this a try after all. – Jimmy Dec 29 '20 at 1:13
  • Thanks everyone for all the big help, Think I understand it now, 100 amp sub panel with #2 or #3 copper from main panel with a 100 amp breaker to main lugs of sub panel, 40 amp breaker from sub panel in house with #8-3 wire feed to to main lugs of 50 amp sub panel in shed, #12-2 wire with 15 amp breakers for light and outlets in shed. – Jimmy Jan 8 at 1:33