Just tried installing a Gosund Smart Dimmer Switch model number DS1. This is a single pole installation.
First issue was that upon removing the old switch I had 4 wires, but 2 were twisted together and connected to the ground screw.
I'm assuming the ground and neutral had been put together? I separated them and connected one to the ground wire and one to the neutral wire of the Gosund, flipped the breaker, and got nothing. So then I swapped the ground and neutral connection, turned the breaker on, and the Gosund switch's lights illuminated.
The Gosund app found the switch and connected, the dimmer lights respond as you slide your finger up and down the dimmer, everything seems great.
Except the light never actually comes on. Manual operation or via the app, the light never comes on.
I have no idea how to proceed.
  • The problem you are running into is when this wire was code a ground wire was not required. Depending on the actual date the receptacles may have been 2 prong non polarized (both holes the same size) and there was no separate ground, later polarized became code with the hot being the smaller. Then again later ground conductors were required followed by GFCI’s and arc fault protection. Today a recent code change allows to pull a separate ground from the panel (you may need it). But you need to reconnect the 2 wires as something down stream may not work now. – Ed Beal Dec 23 '20 at 21:32
  • I have the same issue. Can’t figure it out – user129952 Feb 9 at 0:16
Don't experiment.
The first rule of electrical for novices is don't experiment. Don't just toss wires around hoping for a positive outcome. The reason is simple: lots of combinations will work, but will kill you. So stopping at the first one "that works" is Russian Roulette.
Nothing should be done without knowledge or reasonable expectation. This requires skill and experience, and there's simply no substitute for that. Fortunately you're here.
Now, this started with a cognitive bias: that since Gosund needs certain wires, surely they must be there. Can't assume that.
The two wires that were previously joined need to be joined again. They're not spares, they were already doing a job, and separating them broke that job.
Wires in the box
Cranking the gamma in Photoshop told me a bit about what's going on in the back of the box, but a flash photograph up close could be more helpful. (DO NOT disconnect and splay out every wire - generally every cable comes into a box anonymously, and the data about the function of the wires is stored in how they are hooked up.)
However it looks to me like this is a common 2-cable switch arrangement with supply coming into the switch, and the lamp on a spur. That's good news for smart switches. It looks to me like this is cloth-over-rubber wire, and you must watch that for aging/deterioration, and the maker went to some trouble to make one wire black-ish and the other white-ish.
So that aligns with the two white-ish wires being found already hooked together. I am appalled to see them on the ground screw of the switch, but there might be a reason for that - there may be a viable ground back to the panel, and they may have stolen it if they had a wire problem with the supply-side neutral. Very dangerous but you can't fix stupid.
So my guess is the two "white" wires are neutral. In a typical switch layout, they are already doing a job, so tied together they must remain. A smart swiich neutral can be added to the pair.
Grounds
Safety ground wires are bare, green, or yellow with green stripe. If you don't see that, then it's not a ground wire. However, metal junction boxes, metal conduit and metal armored cable jacket can also be viable grounds. Note these junction boxes are metal.
With metal conduit or metal jacketed cable, ground reaches the box via the fitting. With a ground wire into a metal box, proper procedure is to attach the ground wire to a screw in the back of the box. The metal box gets grounded first.
The metal box can pass ground to switches via the mounting screws and the metal yoke of the switch (the wings that the screws go through). Your switch appears to have a plastic yoke, that is a red-flag. How did UL approve that? Fair chance they didn't -- there's a lot of uber-cheap crud coming out of a certain Asian country, and they market the daylights out of it on Amazon. Look for a UL, CSA or ETL mark with a file number. CE is usually fake, and FCC and RoHS are meaningless. If it isn't approved, back it goes.
Note that you cannot pass ground to a receptacle via the screws, unless they are labeled "self-grounding" (which is all that means; grounding through screws OK)*. In an older house like this, make a habit of using "self-grounding" receptacles.
What I would do
It looks like you either don't have a ground, or it's the metal box. Most metal boxes have a hole tapped for a #10-32 screw, for grounds. Ground wires can be attached there if the box is grounded.
The neutral is the 2 wires tied togeher; neutral gets added.
Now you need to distinguish supply (always-hot) vs lamp (switched-hot). The good news is, guessing wrong here is safe. So pick a black wire from the wall and hook smart-switch supply/Line to it. If you got the right one, the smart switch powers up. Since the smart switch has neutral, it doesn't need the lamp wire to be wired.
Then it's a victory lap to hook up the remaining wire.
* and certain other rare conditions you don't have.
  • Being you are “appalled to see them on the ground screw of the switch” shows you have not been in this business long this was somewhat common just as 3 wire ranges and dryers were back then. – Ed Beal Dec 23 '20 at 21:23
  • I went the safer route and simply bought a "non-smart" dimmer that didn't require a neutral. Put the two original "ground" wires back together on the ground screw and people simply have to get out of their chairs to turn the light on or off :) – jerH Dec 29 '20 at 23:52