UPDATED QUESTION

Thanks all, this is extremely helpful and interesting. I've since uninstalled the outlets and have written up a new diagram to see what you guys think.

(1) I'm removing the 2nd GFCI now that I know it's redundant and replacing with a regular outlet (marked GFCI protected)

(2) No longer daisy chaining. I will splice off A/C line. {Note, A/C is the only item on the load side}

new diagram


OLD QUESTION

I just intercepted an outdoor circuit going to a mini-split 115v AC unit with 2x 125v GFCI outlets. It's a junction box with 2 other circuits in there.

Problem Once wired, both outlets function (outlet tester confirms "correct wiring"), and the AC unit runs. Between 20-90 minutes later, the 2nd GFCI (closest to the load) pops.

Notes

  • 5 ground wires are connected via a red wing. One was previously hanging out but this was fixed
  • Outlet box is covered and weather proof
  • Nothing is currently plugged into outlets (theoretically only thing running on circuit is AC unit)
  • Both outlets pop on occasion but usually the one on the load side
  • The breaker popped once

Photo of line attached. enter image description here

4
  • 4
    That's a nutty way to wire them, with no benefits.
    – Ecnerwal
    Dec 10, 2020 at 3:49
  • 2
    Why are you wiring the second GFCI off the first GFCI's LOAD to begin with?! Dec 10, 2020 at 4:22
  • Did you consider the amperage rating and type of the gfci with respect to your appliance/load and circuit rating? , and i echo similar sentiments with regards to wiring config as above. That may be the problem Dec 10, 2020 at 13:03
  • What do you mean by "I just intercepted an outdoor circuit"? Does that mean you cut into the existing wiring going direct from breaker to AC so you could add outlets without having to install an additional circuit and run more wiring?
    – FreeMan
    Dec 10, 2020 at 13:18

2 Answers 2

4

Sloppy work

Daisy chaining two GFCIs like that is sloppy or ignorant. Such work tends to suggest more of the same. Lots of people install GFCIs with the supply on LINE (because it won't work if they don't) and onward wires on LOAD. They have no idea what LOAD even does, they just don't see any other screws to put them on. So they are putting the downline circuit under GFCI protection without realizing they are doing that. This causes lots of interesting problems.

It's also possible the A/C unit is not the only load on the protected side of that GFCI. There may be other loads, and they may be causing the problem.

Multiple circuits in a box bring a certain risk

...which can be a real nuisance for GFCI installations.

Normal wiring requires each neutral must be monogamous to its partner hot(s). [there is an installation type where 2 hots legitimately share a neutral]. Crossing neutrals in a circuit creates a significant danger, but there's nothing to warn you of having done that, since all neutrals go back to the neutral bar anyway.

However GFCIs will notice a crossed neutral and "enforce it". They trip immediately when any load is placed on the crossed-neutral circuit, because current flows off a different hot but back through the GFCI's neutral, thus causing a current imbalance. So again, it could be a load on that circuit cycling on, and may have nothing to do with the A/C unit.

Outdoors is harsh on GFCI devices

Which is why I don't like putting GFCI devices outdoors. Since I understand how downline protection works, I just place the GFCI device indoors and extend it to plain outlets outdoors.

Whenever a GFCI device provides protection to another device or outlet downline, Code requires a sticker be affixed that says "GFCI Protected". No one installs them lol, which leads people to think GFCI receps are needed when they aren't.

It is possible that weather action and age have killed the tripping GFCI #2. So, given that you know GFCI recep #2 is totally redundant to GFCI recep #1, I recommend replacing GFCI #2 with a plain receptacle rated for outdoors. And put the sticker on it! You can make your own label; I make white ones on a P-touch label maker.

5
  • 1
    I wouldn't describe a mistake due to ignorance as sloppy. It's merely ignorant. We all have learnin' to do.
    – isherwood
    Dec 10, 2020 at 20:59
  • Ha! I never thought of MWBCs as polyamorous before, but I like it! Nice analogy.
    – Nate S.
    Dec 10, 2020 at 23:07
  • 1
    Ignorant it is!! I agree with @isherwood 's definition of sloppy, but still dumb!
    – user126916
    Dec 13, 2020 at 2:18
  • And thank you to everyone! Lot's of learning to do!
    – user126916
    Dec 13, 2020 at 2:19
  • As long as everyone's OK with the 'ignorant' word. I just didn't want to insult! Dec 13, 2020 at 3:51
1

I agree with the comments indicating there is no reason to daisy chain two GFCIs together like you have. I think the root of the problem might be the A/C, since sometimes the breaker trips too, but I would start by swapping out the second GFCI (closest to the A/C) with a regular non-GFCI outlet. You should mark it "GFCI protected" since it is wired off the load side of the first GFCI and gets the GFCI protection and benefits but doesn't need to be a GFCI itself. I think you might still have problems, and if that is the case I would recommend having the A/C unit checked by a technician.