4

This 3-gang box in the kitchen houses a GFCI protected outlet, a dishwasher switch, and a garbage disposal switch. I will be wiring the dishwasher and the garbage disposal from under the sink with a box with two switches. The plan is to remove the wall switches and connect the hots at the existing box.

I’d rather not rip out the wall to remove 3-gang and replace it with a single box that would house the outlet and also act like a junction box for the dishwasher and disposal extension. I am looking at the least “intrusive” ideas that will allow me to do that.

One thought was to cover the two spaces with a drywall and install a single plate.

Another was to somehow pry the 3-gang and drop it inside the wall, then try to install an old-work box.

Any other ideas? What would you do?

This part of the wall is already painted but I guess I’d have to do what I have to do. Should I just bite the bullet and cut maybe a 1’x1’ square, put a proper single box and drywall it, or is there a better way?

enter image description here

6
  • 18
    "this kitchen is impossible to cook in, it just has too many receptacles" said no one, ever. – Harper - Reinstate Monica Dec 1 '20 at 19:32
  • Gotta say, this is very confusing: "I’d rather not rip out the wall to remove 3-gang and replace it with a single box that would house the outlet and also act like a junction box for the dishwasher and disposal extension. I am looking at the least “intrusive” ideas that will allow me to do that." Your question seems to be asking exactly how to do it, even though you say you don't want to. – FreeMan Dec 1 '20 at 19:35
  • @FreeMan doesn’t mean I know what I’m talking about ;) Just asking for opinions. – David Dec 1 '20 at 20:10
  • 2
    Why do you want to downsize the box to begin with? You may just have too many wires there for a single-gang box.... – ThreePhaseEel Dec 2 '20 at 0:02
  • 1
    Do you really mean you're going to put the switches in a less accessible place? That would be frowned upon in the UK. In my kitchen, I have fused switches for washing-machine and fridge above the counter-top, with unswitched sockets ("outlets") behind each appliance. – Andrew Leach Dec 3 '20 at 10:45
26

So I called my sweetie over, who is the resident chef, but knows nothing about electrical, and explained you had extra gang spaces and wanted to eliminate them. Other than that, I did not "lead the question". The instant response: "This, please!"

enter image description here

See, now that's the difference between an electrician and a chef.

I've learned to be careful and avoid the "target fixation" which motivates many to do wiring that exactly complies with Code minimums... or is designed to min-max for minimum cost. We don't work for electricity. Electricity works for us. Usability is the reason we wire, not Code... and as for cost, most electrical stuff is laughably cheap compared to its value.

11
  • 2
    That's a way to turn a bug into a feature! – manassehkatz-Moving 2 Codidact Dec 1 '20 at 20:18
  • 2
    @FreeMan Pigtails are free when computing cubic inch volume of wires. Yokes are not free, but there are already 3 yokes in the box. – Harper - Reinstate Monica Dec 1 '20 at 21:19
  • 3
    @harper-reinstatemonica This is increasingly the most desirable option for me. Nice Photoshop skills by the way. On the pigtails, would you pigtail the other two from the original one or pigtail all three? – David Dec 2 '20 at 4:13
  • 5
    BTW, @David, this isn't Photoshopped. Harper went all out and built a mock-up of your kitchen based off your picture and wired in the three switches. For a small fee, he'll ship the whole pre-wired wall to you 'cause that's the kind of guy he is! :D – FreeMan Dec 2 '20 at 19:46
  • 5
    @David I work in stranded THHN so I pigtail for those reasons. In your shoes, I would use any old way that works, since I'm very comfortable troubleshooting. If you buy the $3 receptacles instead of the cheapies, they have a feature called "screw-and-clamp" that lets you back-wire 2 wires under each screw (you tighten the screw to clamp - HARD). That means any (non-split) outlet can take 4 wires :) You could use that as a hub :) – Harper - Reinstate Monica Dec 2 '20 at 19:48
7

The easiest solution is to pull the switches, connect the wiring, using the space in the box as your junction box, and put on a 3-gang, 2-blank cover plate. The added bonus is that if any future person (including future you) needs a location for a switch or extra outlet, they've got it with almost zero work.

If that's not an acceptable option (and I understand that it may not be), the hardest part of downsizing the hole is taping the drywall and getting the joints smooth. So from there, it probably doesn't matter a whole lot what approach you use.

The most important item is to ensure that you do not exceed the box fill requirements when connecting all your wiring in the new single-gang box. There are questions here about calculating fill, and you could ask a whole new one if you're not sure. If you've got too much fill, you'd need a 2-gang box, and if that's the case, it makes leaving the 3-gang look even better.

To actually replace it, I see a couple of options, depending on what the box is made of.

Option 1 - metal box

  • You'd most likely have to open up more drywall to be able to get the nails/screws out.
  • Open it from stud to stud so you've got something to attach the drywall to on both sides to make the repair easier.
  • Remove the old box
  • Install a replacement new-work box
  • Install a piece of 1x2 next to the new-work box screwed into the drywall above & below the opening
  • Install a drywall patch from the 1x2 to the exposed stud, screwing it into wood on both ends
  • Tape, mud, sand, paint

Option 2 - plastic box

  • Remove the fixtures
  • Using an old screwdriver and hammer or extremely careful application of an oscillating cutter, destroy the old box in place.
    • I've done this - it is possible. You need to use great care to ensure you DO NOT cut or nick the sheath on the wiring.
  • Remove the pieces as you break them off
  • Use the oscillating cutter or a Sawsall™-type saw to cut nails holding the old box to the stud.
  • Install an old-work plastic box next to the stud
  • Put a piece of 1x2 behind the existing drywall, screw it in above and below the opening
  • Screw in a patch of drywall to the 1x2
  • Tape, mud, sand, paint

Option 3 - plastic or metal box

  • Cut a large enough opening in the drywall to get a hammer above and below the box to pry out the nails holding the box to the stud
  • Cut the opening wide enough to span from the near stud to the next stud
  • Install a new-work single-gang box
  • Install a drywall patch, screwing it into the stud above and below the new box and to the next stud over
  • Tape, mud, sand, paint

Option 4 - metal box with conduit

  • Depending on where the conduit enters the box, you may have to replace bent conduit with straight conduit, but otherwise, it's like Option 3, but with more drywall removal/replacement

Again, the hardest part of all of these is the last step: Tape, mud, sand, paint. Once you decide on an action that involves opening the wall from stud-to-stud, you don't have significantly more work to do in this finish step, so it probably doesn't matter which one you choose.

The key item is to ensure that you do not over fill your new box with wiring - something that's more likely if you've got #12 wire instead of #14.

8
  • 3
    You can also fit a reducing (or Step-down) mud ring (3-gang to 1 gang) if you want the "only one space cover plate" - but otherwise you'd leave the box alone. Patch over the ring and away you go. – Ecnerwal Dec 1 '20 at 18:36
  • @FreeMan, wow, a nice answer! Going with blank is not appealing, so I am left with drywall work and then, no small is too small or big in this case, I will probably go with Option 3. The wires are 2x #12s and one #14, and I will be using is one of those brown Reinforced Phenolic boxes with 18 cu in capacity. Do you think 1’ high drywall cutout (stud wide) will be sufficient to do the work? – David Dec 1 '20 at 18:40
  • @ecnerwal that’s an option but I just looked up 3 to 1 gang step downs an they are $50+ a piece, whoah! And still have to do mud work. – David Dec 1 '20 at 18:44
  • 2
    Price the labor savings of NOT ripping out and replacing the box, or re-consider the "two blank one switch" cover plate for labor and money savings (no drywall repair, even) – Ecnerwal Dec 1 '20 at 18:47
  • 1
    @Ecnerwal Write that reducing ring up as its own answer and you've got my vote!!! That's much easier than any of what I said (except putting a blanking plate over it). – FreeMan Dec 1 '20 at 19:36
3

You can also fit a Reducing (or Step-down) mud ring (3-gang to 1-gang) if you want the "only one space cover plate" - but otherwise you'd leave the box alone. Patch over the ring and away you go.

While somewhat costly in the abstract, the time and effort you save not ripping out the old box, installing a new box, re-terminating all the cables, etc. is significant - as is the ability to "undo" with little work if you change your mind.

Mind you, I think you'd be better off with an additional receptacle or two and a 3-gang cover plate with as many blanks as you don't add receptacles, but I'm not you.

1
  • The box likely is sticking out too far for a mud ring to work. At the very least it would have to be pried loose and shifted deeper into the wall. – Hot Licks Dec 2 '20 at 19:41
-3

In your second sentence, it sounds like you wanted to say, "outlets", not "switches". If so, then that is the correct approach. These new appliances are 15 amp rated, they should have separate breakers, and can accept with 14-2 wiring. However, municipal codes often require thicker 12-2 electrical wiring in all kitchens (referring back to older days when kitchen appliances all took 20 amp breakers), so you should check with them to find out what is acceptable. Of course, never use GFCI outlets behind the counter (only use traditional outlets). GFCI's are for above the baseboard (above the countertop), and on exposed walls. When wiring GFCI outlets, only use the top of the outlet (never break the tape and use the bottom of the outlet, or you will trip the breaker). If you do this, your wiring is a breeze, and everything will work right.

2
  • 1
    Can you provide a code example of requiring #12 wire on a 15 amp circuit? Also, please clarify what you mean by differentiating "behind the counter" and "above the countertop". Finally, the other set of contacts on a GFCI outlet are designed to be used or they wouldn't be included. There is a very specific way in which they should be used, but saying "never" because it will trip the breaker is flat wrong. – FreeMan Dec 2 '20 at 12:29
  • 3
    No, I meant switches. I will be essentially relocating the switches from the walk to under sink junction with shut off switches. The GD will be activated via air switch. The GD wire is a #14 with 15A breaker and I believe that is quite sufficient. The The two DWs will have their dedicated 20A circuitry with #12 wire. The GB was already wired with #14 wire before remodel so it’s an old work. House is under 20 years old and wiring is to the code then. – David Dec 2 '20 at 13:54