Suppose I'm wiring a 100 A subpanel, which receives my two phase wires (black, red/black), my grounded/neutral wire (white), and my ground wire (bare) from the main panel. Since this is a subpanel, the green bonding bolt isn't installed, and so the subpanel neutral and ground terminals are not bonded in the subpanel.
My question is, back at the main panel, are there any constraints on where can I tie the grounded/neutral and ground/bare wires from the subpanel? The main panel has a grounding bar along one side and the usual neutral/ground bars on either side of the breaker rows. Can I connect my grounded and ground wires to any ground/neutral bar in the main panel, since they're bonded in this panel, or must I land the wires from the subpanel on specific bars? Seems like it makes no difference in terms of safety, since neutral and ground are bonded in the main panel and at the same potential, but maybe there's a 'gotcha'. Any advice?
    White is neutral. It is not grounded at all. Neutral is not ground. Ground is an emergency fault catcher only. Neutral is the normal and routine current return. Conflating them leads to huge mistakes. Dec 1, 2020 at 5:18
  • I don't have it in front of me, but in reading through Wiring Simplified, 42nd Ed., I'm 99% certain the authors refer to the neutral wire as the "grounded" wire, the bare wire as the "ground" wire, with "grounding wire" referring only to the wire attached to the ground prong of an appliance cord. Does this naming scheme only work in the context of a main panel?
    – Bort
    Dec 1, 2020 at 20:57
    That's the trouble with reading docs intended for electricians lol... that's straight out of NEC, which has the very bad nogood habit of referring to neutral as the "groundED conductor" and in the very next sentence will say "groundING conductor" to refer to safety ground. This confuses people constantly, even 50k rep experts here have been seen misreading NEC because of that language. Avoid it at all costs. Dec 1, 2020 at 21:58
  • Hah got it. Thanks for the insight.
    – Bort
    Dec 2, 2020 at 2:27
Neutral needs to go to the neutral bar.
The purpose of neutral is to be the normal path for return current which flows as part of the circuit's operation. As such, it can only go to the neutral bar, since only that is rated to handle that current continuously and on a routine basis.
Safety ground certainly can't do that. Think about it, that bonding screw in the main panel, is that a 4/0 AWG screw?? :) No, it's 10-32 and steel, which is a several times worse conductor than copper. That bonding screw was never imagined to handle normal service currents.
That's why you can't land any neutrals on grounding bars and other facilities intended only for safety ground.
Safety ground is not used for anything; it only handles fault currents for the duration of a ground fault (i.e. long enough to trip the breaker). Ergo it does not need to be rated for continuous service current.
  • Avoiding a return path through the bonding bolt makes good sense to me. Thanks.
    – Bort
    Dec 1, 2020 at 20:52