I just had a electrical inspection stated 2 hot 1 neutral and one ground needed.
I thought all of that was there.
meter box n breakerbox
Here are the inspection forms. I have no clue what is wrong or what is correct.
  • That's a PVC conduit exiting out the bottom, correct? Also, what size is that grounding electrode conductor (single bare wire) that exits out the bottom of the meter-main, and is that PVC conduit run continuous to the house, or does it terminate somewhere underground? Nov 15 '20 at 20:49
    Please consider merging your unregistered and registered accounts, which will allow you to edit, comment on any of your posts and most importantly accept an answer on your question. Thanks, and welcome to the site!
    – Niall C.
    Nov 15 '20 at 21:35
You are being written up for a missing Equipment Grounding Conductor (EGC) which is the ground wire that goes with hots and neutrals in every circuit or feeder.
The thing between this meter-main and your house is feeder not service wire. Above the meter is service wire. Feeder requires EGC, service does not.
What I see
is 200A service coming from the top.
I see a bare wire that is part of the Grounding Electrode System which bonds the meter-main chassis itself to local grounding rods. However this is not an EGC ("ground wire") and does not go anywhere an EGC needs to go.
I see the main feeder going into the lower pipe in 3 wires. I see no ground wire (EGC), so yeah, the inspector got it right.
Fire your electrician. What were they thinking?
If the power company installed this feeder, that would be why. They follow a different codebook (NESC) and they're not used to working in NEC rules. They make this mistake all the time.
Some people think that if the pole has a ground rod (GES) and the house has a ground rod (GES), they don't need a ground wire (EGC) also, because there's dirt between the two. Um... dirt doesn't conduct electricity that well :)
What to do
You will need to add an appropriate sized ground wire to the pipe. If the hot wires are exactly #2/0 Copper or #4/0 Aluminum, you can use a #6 Cu or #4 Al ground wire. (However, if the hot wires are larger than that, the ground must also be larger, forcing you to #4 Cu or #2 Al).
The added wire can't exceed conduit fill limits. The ground wire can be bare if it's copper, which helps with conduit fill. It's OK to use aluminum hots + copper ground.
You can fish just the wire if you can successfully get a fishing tape down that conduit with the wires in there. If not, you'll have to pull the 3 wires and then pull them back in with the 4th wire.
  • "in 3 wires" is bolded, so that's important, but why? Should the main feed be a cable, not individual wires? There is a ground, but it appears to exit the box via its own hole and, presumably, goes to the ground. I presume there should also be a ground going down the conduit to whatever this is feeding?
    Nov 16 '20 at 18:55
  • @FreeMan didn't see your comment because I was doing a major edit that may address your issue. Nov 16 '20 at 19:30
  • "cable" isn't necessary, but it needs to be "4 wires" because the ground from meter-main to panel is missing. Got it. Thanks!