The breaker for my microwave tripped and when I turned the breaker back on it tripped again after using the microwave again. I tested the microwave in another outlet and it works fine. I went to replace the outlet and I found a black wire, two white on the same side, and ground. I turned off the breaker and tested the wires only to find that one white wire still has 120v where all other wires are dead. Why is that wire supplying voltage on the neutral side?
2Are there other things on this circuit? Can you post a photo of the inside of the box please?– ThreePhaseEelNov 15, 2020 at 1:32
Is the breaker that trips a simple breaker or does it include AFCI or GFCI?– manassehkatz-Moving 2 CodidactNov 15, 2020 at 1:39
It sounds like some other circuit is poaching neutral from this circuit. Also, are there red wires in the box?– Harper - Reinstate MonicaNov 15, 2020 at 2:05
1the red wire?– manassehkatz-Moving 2 CodidactNov 15, 2020 at 3:39
How old is your house?– Alexis WilkeNov 15, 2020 at 21:18
1 Answer
You could be dealing with 1/2 switched receptacles. 1 part of the receptacle is controlled by a wall switch that will allow table lamps and etc to controlled by that wall switch. My whole house is wired that way. Half the receptacle is wired always hot and the other is controlled by a switch. Check it out.