0

120V only, 100 amp panel in the shed. Tying in to meter box at the house. Six 120V outlets/2 small ceiling fans/can lights and a small 120V plug-in heater.

What wire will result in the electrical inspector saying, "No problem"?

2
  • 2
    Consider the inspector might want to see the trench before you back-fill it. That's to determine if you really did the work of digging to the required depth for your choice of conduit/cable -- for example, some types of conduit can be as shallow as 6" or 12" while others need to be at 24" depth. You may not have the option to fill it up before the weather hits. If it gets full of water, pump it out if needed. Commented Nov 8, 2020 at 22:18
  • Since you'll probably want to just do it once, I'd say run the same gauge as your house currently does. Be prepared for any future use :)
    – rogerdpack
    Commented Nov 8, 2020 at 23:33

4 Answers 4

9

Just drop a conduit in there instead, you'll thank yourself later

Instead of rushing to buy wire and getting the wrong thing, then having to dig it up later, why don't you get yourself some fat PVC conduit (such as 1.5" or 2") and lay that in the trench instead, with prefabricated sweeps and expansion fittings at each end? That way, you can pull the wire at your leisure, and don't have to worry about digging things back up if you want to upgrade later. While you're at it, you can also lay a second conduit, say 1", if you want to to provide a convenient way to run a telecom cable (of any sort: phone, Ethernet, fiber, you name it) out to the shed.

5

You're in a hurry (which is rarely good) and you're making some absurd choices (or you don't understand how things work, same difference.)

I doubt you'll find a 100 amp single pole breaker.

If you need 100 amps at 120 volts, then 50 amps at 240 volts is how that happens in the USA/Canada. Your panel at the far end can be 100, 125 or 200 amps (the 50A protection will come from the feed breaker, the main breaker at the shed is just a local shutoff, so "more than 50" will suit, and larger panels come with more spaces.)

Your panel at the far end gives you the 120 volt outputs you want, from the 240 volt feed.

Happily, you can do that on 3 2AWG aluminum wires plus a #8 or 10 copper ground wire. Way less than 4/0. But you absolutely need 4 wires, not 3.

1-1/4" (or larger, which gives you more options) schedule 80 conduit would let you fill the trench today and worry about buying wire later.

3
  • Why are 4 wires needed, not three?
    – Yehuda_NYC
    Commented Nov 8, 2020 at 23:52
  • 1
    Hot, hot, neutral and ground. 3-wire feeders for accessory buildings have been forbidden by code for decades, and I address the "110V only" (sic) aspect in the second and third segments of my answer, so there are two hots here.
    – Ecnerwal
    Commented Nov 9, 2020 at 0:05
  • 1
    @Yehuda_NYC two hot, a neutral, and a ground, as described to run 240v instead of 120v.
    – Moshe Katz
    Commented Nov 9, 2020 at 0:06
3

Realistically, you don't know nearly enough to be able to select a legally valid cable, and you won't be able to learn enough fast enough to make a decision with confidence.

As such, I strongly echo ThreePhaseEel's advice of "throw a fat conduit in there and figure it out later".

You only need to glue the 3-4 segments near the ends. There's no point trying to make conduit watertight; it's gonna fill with water no matter what you do :)

If conduit just doesn't work for you, toss in 4-wire cable sized 1/0 aluminum or 2/0 aluminum. The ground wire can be smaller but MUST be there. You really don't have time to get red-pilled on why aluminum is perfectly fine for feeder, but mark my words, you will regret using copper wire.

There's a bunch - a bunch of skilling up to do later. But if 1/0 or 2/0 4-wire Al is in the ground, we can work with that.

2

I deleted my original answer because the others were more specific & complete. Except for one thing:

Pull string:

Pull String

This is especially important for long runs and for outside may fill with water before you get a chance to pull the wires through runs. Pull string is dirt cheap. I would put 2 strings in, with several feet extra on each end outside the conduit. That should make the eventual pulling very easy. Actually maybe even put in 4 - one for each wire. And maybe a spare. Or you can tie extra string on with each wire you pull through, so that you pull through the string for the next wire, though with conduit (as opposed to an open wall pulling a bunch of low-voltage wires, which is what I more often have to do myself) you are probably better off pulling all the wires at once.

Bottom line is: pull string is cheap, struggling to get wire through 300' of water-filled conduit without a pull string is a lot of unnecessary work.

2
  • 3
    My personal experience suggests that this is not a big deal. A wet/dry shop vac will suck water as well as string. Heck, on one really troublesome run, I sent the string through tied to a foam plug (aka mouse) driven by a garden hose (I needed more pressure than suction would give me. The geyser when it got through was amusing.) And you want to pull all the wires at once - adding wire to a conduit with wire(s) in place is much harder than pulling one bundle into the conduit.
    – Ecnerwal
    Commented Nov 9, 2020 at 0:00
  • 2
    For pulling in conduit, most of mine is as well. The tendency of the first cable or wire to twist makes the theory of a trouble-free pull for the next cable dubious at best. I've certainly had the experience where we had to pull out what was in the conduit, add a wire, and pull it all back in, because it simply would not go as an added cable, but the whole mess fed in together went fine. I've gotten away with adding cables in other cases.
    – Ecnerwal
    Commented Nov 9, 2020 at 0:10