I am installing electric floor heat in my bathroom. It will be on a dedicated 120V/20amp circuit. The breaker has a GFCI. I am using same manufacturer for thermostat as floor heat. The thermostat is a 120 Volt stat that is connected to the line and load. . The thermostat includes a integral GFCI. The thermostat's GFCI has a end-of-life feature to isolate the heating cable load. Question: Should I keep the system with 2 GFCI's or should I replace the breaker GFCI with a regular breaker? I can't disable the thermostats GFCI.

4
  • Basic answer is just use one gfci. But hang on a bit and Harper will add his tripping picture. Commented Nov 1, 2020 at 22:16
  • 2
    What do the manufacturer’s instructions say?
    – nobody
    Commented Nov 1, 2020 at 23:42
  • Note that you may need an AFCI breaker for this, depending on what NEC edition your AHJ uses Commented Nov 2, 2020 at 0:03
  • 1
    mana' is referring to this :) which might also answer your question. Commented Nov 2, 2020 at 1:43

1 Answer 1

1

I would not put a GFCI breaker on this device. Code requires it to be GFCI protected and 2 GFCI devices can cause trouble in resetting.

I ran into a issue with one of the floor style that ran a self test that would trip the breaker so we could never reset it (the home owner called me I megged the heater and it was good so then I pulled 1 lead to the heater still tripped the panel breaker, called the mfg and they told me it was in there GFCI test that was tripping the circuit. I believe this test was the end of life test where it basically megged the circuit prior to energizing looking for leakage that may not show up on a standard test until wet.

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.