I have a 240 volt circuit feeding a water well and want to "split off" a 110 circuit for a light and small heater. The well has a safety break of 13.2 amps max. The wire is apx. 100 feet long, 8/4 with a 20 amp breaker. Can I add a load center at the well, use a 20amp,240 volt breaker for the well, 15 amp breaker/120 volt outlet (or 2, 1 on each leg) utilizing the neutral wire back to the original load center. Currently it is protected by a 20 amp breaker, will a 30 amp breaker be too too much for the 8/4 wire? Thank you,

  • How small is your "small heater"? – ThreePhaseEel Oct 28 at 23:48
  • Still undetermined, trying to balance the available power with the heat needed – Sam Oct 29 at 3:16
5

By NEC you typically could. You would need to add a ground rod if you don't already have one. A single circuit doesn't require a ground rod, a panel will.

I would throw a little caution here, my well isn't too deep, only 200 feet. I have a 1.5 hp 10.6A motor controller says 12A pump max. Well is 200 ft from the service, that's 400 ft of wire. Voltage drop calculators say 4% voltage loss on the wire. So pump and a few cfl or led lights, I'm good to go if I have 8/4 aluminum.

Add 4A of heat, I get 3% voltage loss to the pump house and another 3% down the well. That is outside of the NEC recommendation of max 5% voltage loss, and that's not even considering the inrush on a motor that is fully loaded on startup. Change that 5A of heat to a 12A heater, I'm not good to go any more. Legal, but could still be problematic.

| improve this answer | |
  • @Ecnerwal, I just found out the well is 416 feet deep, plus the 100 ft from the service to the well. The wire is 8 gauge copper and the ground wire goes into the well with the other wires so I don't know if or where it is connected. How many amps can I realistically and safely add? – Sam Oct 28 at 18:13
  • With copper you are are in good shape, probably even for a 1500w, Your 416 feet of well loses about 3%, and you lose about 1% going to the well. Adding a 1500w 120v heater will add about 2% loss on that one leg, making a 2% loss to the well measured leg to leg. That puts you right near 5%. Some think 5% is artificially conservative, but you will have a much bigger loss during motor starting that will push that short term voltage loss much higher. – NoSparksPlease Oct 29 at 0:54
8

Assuming it's 8/4 copper wire, you could even use a 40A breaker to protect it - if aluminum wire, 30A.

You have a 4-wire feed, and you'll need to isolate the ground and neutral in the sub-panel. If your well casing is metallic, presumably it's already tied into the ground wire - if not, it should be (they make one heck of a ground rod.)