I have an old electric 240V baseboard heater. Currently, it is using 2 single pole 20 amp breakers. I am going to change that to a 1 double pole breaker. No neutral is used. Is GFCI and/or AFCI breaker required? Does such a breaker even exist?

3
  • GFCI may depend on location (e.g., garage or basement might need it, where other rooms probably not). AFCI very likely needed where GFCI is not. However, a lot depends on version (year) of NEC used in your area. Plus simple breaker replacement (which is a good idea, 240V should always be double, not 2 single) may not trigger need to upgrade to GFCI/AFCI. Location (city/state)? What room in the house? – manassehkatz-Moving 2 Codidact Oct 22 '20 at 17:17
  • It is in an office room, location is NY (not NYC) – Andrew Oct 22 '20 at 17:19
  • That puts you (as far as I know) on NEC 2017, and likely not GFCI, but possibly AFCI. I'll let the real experts give an actual answer. – manassehkatz-Moving 2 Codidact Oct 22 '20 at 17:24
2

You need to handle-tie those 2 breakers, boy howdy! If you can't find an appropriate factory handle tie, use a 2-pole breaker.

You don't need to GFCI a 240V circuit; the only exception being if you're in NEC 2020 territory (about 4 states so far) AND the location is one that normally needs GFCI (garage, basement, kitchen, bathroom etc.)

AFCI protects the wiring from arcing, which can cause house fires. Unfortunately 2-pole AFCIs are scarce. NEC is not in the habit of requiring use of products which do not exist in the marketplace, so you're in the clear on that.

However if you want it, you might get lucky with your panel's brand. For instance GE's latest AFCIs do not need neutral wires and are specifically designed to be used in pairs with a handle-tie for 240V circuits and MWBCs. But you can only use those in GE panels.

You cannot use brand X breakers in your panel, only your own brand, or Eaton CL, Eaton CHQ or Siemens QD which are UL-approved for competitor panels. However none of those offer anything special in the AFCI space.

3
  • OK, I will see if one is available for my panel or go with a regular breaker – Andrew Oct 22 '20 at 18:19
  • You don't need to GFCI a 240V circuit in an office even under the 2020 NEC, as it didn't change where GFCI protection is required, only what types of outlets use it – ThreePhaseEel Oct 22 '20 at 23:46
  • @ThreePhaseEel Oh, thanks. – Harper - Reinstate Monica Oct 23 '20 at 14:16