2

The natural gas venting tables talk about lateral versus vertical rise and pipe diameter, plus the 2 and 10 ft rule for height above the roofline and outdoor vertical walls but they never mention how much of the B-vent can be above the roof versus inside the attic or conditioned space.

In my case Im moving a 40 gallon natural venting gas water heater into the unconditioned attic with only 3-4 feet of headroom before I need to penetrate the roof at which point I must be 2 to 2.5 ft above the roof for a 9/12 pitch roof. That means I will have maybe 7 feet of total vent (straight up).

The attic isnt conditioned but its not freezing cold in winter either. Will 2 feet of b-vent exposed to ice cold winter air cause issues on a short run of 3 inch B vent?

Maybe its irrelevant since its an unconditioned attic to start with....

2

Let me answer my own question as this might help someone else.

After much research and back and forth with Amerivent (thanks Karen O.)tech support I've learned that they feel the SELKIRK guide is the definitive guide on venting and as per that guide, 5 feet is the minimum vertical (only) height for B-vent with 6 feet recommended and that it doesn't matter if its conditioned or unconditioned space. And of course how high you have to stick up out of the roof penetration is of course dependent on slope and proximity to vertical surfaces and the roof itself, not including other combustion vents.

http://www.selkirkcorp.com/~/media/selkirk/reference-documents/common/file/product-literature/venting/selkirk-rv-type-b-vent/selkirk-sizing-handbook--application-guide.pdf

This gentleman also has some nice pictures and explanations. He doesn't advocate for no-caulk vent flashing boots but according to Oatey they are B-vent rated. (I'm gonna use an Amerivent storm collar with high temp silicone sealant above that Oatey no-caulk vent pipe boot as well) as a precaution.

http://www.summerville-home-inspector.com/comment/reply/129?device=desktop

Also, don't use the generic vent cap Home Depot sells from Amerivent. Use the lock on kind you can get from Amerivent online.

https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1

Also I've read on Inspectopedia that 16 inches apart for adjacent chimneys is the minimum and obviously you need to leave enough room for the new flashing not to interfere with the adjacent chimney's old flashing.

1
  • Excellent job and more than acceptable to answer your own question! Please be sure to also click the check-mark so others know that this has a resolution. – FreeMan Sep 29 '20 at 15:35

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy