Problem! I have a 1.5 hp 230 VAC deep well pump on a 30A circuit breaker wired with #8 copper that runs a couple hundred feet to the pump controller. Pump specs say it draws 9.7 amps and allows 808 feet of #8 service panel to motor. I now have a Firman H08051 Dual Fuel portable generator (10K/8K gas; 9050/7250 LPG) with the intent to run on propane. The generator has a L14-30R Receptacle to connect to a Reliance 306CRK Manual Transfer Switch that came with a 10' cable of 4 conductor 10 AWG cable. The generator inlet box has 3' of #10 wire to the transfer switch, and the transfer switch adds 3' of #10 wire to the service panel. So the question is, can I power this 30 amp circuit with #10 wire when it's using #8 wire out to the load? And if I can, what is the best connection going from #10 to #8?
1 Answer
You should be OK. The ampacity of the 8 ga is 40 amps, but who ever installed it was considering voltage drop over that long a run and used 8ga. A wise precaution and someone who actually followed installation specs...nice!
The ampacity of 10ga is 30 amps and such a short run between the generator and xfer switch won't have any appreciable voltage drop.
Most of the experienced electricians here don't really like the type of transfer switches you are using. They are over-priced for what they do and there are better alternatives, like a mechanical interlock on the main panel between the main breaker and the generator breaker. That way there is very little re-wiring to be done and you can easily pick and choose which, of all your circuits, are powered at one time simply by turning off existing individual breakers.
If you carry on with your xfer switch, there are tons of easy options to connect 8 ga with 10 ga.