Since this air handler / furnace has overcurrent protective devices in it, would my wiring from the panel then be a feeder or branch circuit?
I kind of think it would be a feeder circuit. And that would mean I have to obey feeder rules. But since this is part of the unit, I'm not sure.
  • This air-handler uses electric heating elements (strip heat) I take it? – ThreePhaseEel Aug 19 at 22:54
Since you have breakers there it would be a feeder. A branch circuit : the conductors between the final overcurrent device protecting the circuit and outlets. In article 100 definitions see exhibit 100.7 commentary is the direction from the feeder definition.
| improve this answer | |
  • A question for educational purposes (my education mostly!): What is the effective difference between a feeder and a branch circuit in these circumstances? Is it bc the receiving device has overcurrent protection? As in if the furnace has a breaker, the cable is a feeder, but if it doesn't it's a branch circuit? – George Anderson Aug 19 at 17:28
    @george Anderson, that is basically it the definition of a feeder is not as clear but points to the branch circuit definition and examples exhibit 100.7 of the code book. Branch circuits go to the devices where a feeder goes to a branch circuit overcurrent current Device. Like a sub or in this case the multiple breakers for electric heat. – Ed Beal Aug 19 at 18:08