0

I have a receptacle in the middle of a series of receptacles, it has line in and load out to the next receptacle (no pigtails). I need to add another outlet near this receptacle and due to placement this is my only option.

What is the best way to do this? Should I strip some 6" pieces and pigtail the charge, neutral and ground wires at the line end of this receptacle? Or should I pigtail the load end and make this receptacle feed two others simultaneously?

Also, while the current series is all 12/2 (on a 20amp circuit breaker), I'm thinking of using a GFCI 15amp as the new outlet, can I just run 14/2 to the new outlet?

This image shows what I am trying to do (notice the last outlet says "new"), except the last outlet will be GFCI.

(https://i.stack.imgur.com/o09Ej.jpg)enter image description here

  • You have some misunderstandings that cause me concern about your level of knowledge. For one, you're using the terms line and load incorrectly. That could leave portions of a GFCI protected circuit unprotected. For two, you seem to think that a 15 amp outlet acts as a circuit breaker or current limiter. That isn't true. You should probably do some reading in a good house wiring book before proceeding. – isherwood Aug 16 at 13:13
  • You are right, I am not an electrician and not well versed in the correct terminologies and lingo. But I have wired in outlet and lights myself. The "line" and "load" references are to the screw connections on the outlets, thats exactly what they are called and engraved as on all outlets I have seen. – 0pt1m1z3 Aug 16 at 13:16
2

I use the words "supply" and "onward" to refer to the two types of cables coming into an electrical box. I don't use Line and Load, because those terms are special where GFCIs are concerned, and careless use of them leads to disaster.

LINE and LOAD: Just use LINE.

You say every receptacle you've ever dealt with has LINE and LOAD plainly marked. That means you're only dealing with GFCI receptacles.

Virtually all GFCI receptacles have a feature that allows 2 wires on the LINE screws. (If you need more, you can always pigtail).

GFCI devices have a very special feature called "Downline Protection". It allows the GFCI device to confer GFCI protection to additional loads that are fed from it. So for instance if you had a GFCI recep in a bathroom, it could protect a light inside the shower stall. This Downline Protection feature should not be used casually or carelessly. It should never, ever be used unless it is your specific intent to do that.

To protect a downline load, attach them to the LOAD terminals. LOAD terminals should never be used for any other purpose. That is why they put warning tape on them.

When you protect a downline load, there is more work to do. The downline load must be troubleshot to assure there aren't pre-existing ground faults or miswiring. Any receptacles must be labeled "GFCI Protected" (and also "No Equipment Ground" if that applies). These markings are mandatory, and are part of the act of protecting a downline load. Ignoring this is a Code violation, and will get you written up at sale time. Again, LOAD should never be used except for that purpose.

Of course you know what happens :) Novices just slap the extra wires on LOAD and they don't even know what they are protecting, so they do not label those extra outlets. They don't even know that they are protecting, so they are flummoxed when the socket just quits working. Many call electricians only to be "led by the nose" to a GFCI they themselves installed. Whoops!

Part of my own "GFCI Protected" labeling is a statement of where the GFCI device can be found.

I'm fond of saying that warning tape says "Do Not Use. For Wizards Only". A wizard being someone who has learned to wield the downline-protection tech correctly.

...Or, do use LOAD. Deliberately.

Between what you already knew, and what you read between the lines above, I gather you have figured out the downline-protection stuff. Congratulations, wizard!

Now... Use it when you want to, and when it makes sense.

If it best suits the situation, you can put one of them on LOAD and the other on LINE. Or both on LOAD - this doesn't require a pigtail because the LOAD wires also can accept 2 wires under each screw (read the instructions to see how).

If you want to put both on LINE, given that there is already a wire on LINE, that would be three, so you'll need to pigtail.

Also revisit any past installations and move LOAD to LINE everywhere (except places where you specifically want downline protection). In particular, eliminate any instance where LOAD of one GFCI feeds LINE of another. That will cause major annoyances.

Watch out for box fill cubic inches

Now the box has finite size. There'll be a practical issue fitting the wires and also a GFCI device, but there's also a statutory issue. Given that your wire size is #12, you must allocate 2.25 cubic inches for each hot and neutral wire.

  • Pigtails are free.
  • All ground wires together count as one wire count.
  • A "yoke" (read: receptacle or switch) counts as 2 wire counts. Yes, really; it counts the same whether it's a small 1-way switch or a fat GFCI.
  • If cable clamps intrude into the box, all of them together counts as 1 wire count.

So I count 6 for your hots and neutrals, 2 for your yoke, 1 for ground. That's 9.

9 x 2.25 cubic inches = 20.25 cubic inches (or 22.5 with cable clamps).

Look around in the back of the box for a stamp indicating number of cubic inches in the box.

If you are beyond statutory maximums, or beyond practical maximums, you can get a box extension. One of my favorites is called the Legrand Wiremold Surface Conduit Starter Box. It's made to give a 1" lift so you can run surface conduit off of the box, but if you just use it for the 1" lift, I won't tell ;)

If the breaker is 20A, then #12 wire. End of subject.

You can't come off a 20A circuit with #14 wire. Not allowed.

If you're thinking "tap rule arcana" you need to read a lot more closely; that only applies to industrial applications in metal conduit etc. If you're in metal boxes, you're really in trouble on cubic inches lol.

If you're thinking the 15A GFCI device will somehow block >15A, no, it doesn't have any ability to do that. As a matter of fact, it is specifically made to pass 20A. UL requires every 15A rated receptacle be able to passthru 20A. That matches a Code rule allowing 15A receptacles on 20A circuits. That is so consumers and electricians only need to stock/buy one kind of receptacle for ordinary stuff.

Or, if the circuit is allowed to be 15A (kitchen, laundry and bathroom receps are not), then you can downgrade the breaker to 15A and run #14 as much as you please. This, however, invites some goober to see the #12 wire in the panel and think it's OK to up-breaker to 20A.

| improve this answer | |
  • Thank you for your detailed response. I'll admit that my question was haphazardly put together and then I got needlessly defensive when my novice knowledge was challenged. – 0pt1m1z3 Aug 16 at 20:08
  • Follow-up question: Since I can connect two LOADs onto a GFCI (primarily to avoid the space issue with one too many pigtails), can I use a GFCI outlet at the current location and derive two loads, one for the existing outlet and one for the new outlet? Mind you the new outlet will be outdoors (with a proper box and in-use close cover). I have read that when GFCI protection is required by code, it can be upstream or even in the breaker, not necessarily in the outlet itself. Or did I misread something somewhere? – 0pt1m1z3 Aug 17 at 19:13
  • @0pt1m1z3 Yes, you seem to understand it. Having an outdoors plain recep protected by an indoor GFCI is always a good plan because it keeps the GFCI out of the weather. Be sure to label reset location, or you will lose your mind later when you need to reset it. – Harper - Reinstate Monica Aug 17 at 19:17
  • Thank you again. Now for the original indoor outlet that the GFCI will feed... what if that were to be on the LINE end and not LOAD (like the outdoor outlet)? I am assuming that would fine, just that additional indoor outlet won't have the downline GFCI protection. I guess I am still unsure why GFCI's allow 2 wires on the LINE end. Is that to simply extend the circuit without using pigtails, much like a standard outlet, which does the same but with two screws? – 0pt1m1z3 Aug 17 at 19:39
  • @0pt1m1z3 GFCIs support 2 wires on the LINE end because most sockets have 2 black and 2 white wires in the box. You don't want to force people to stick the downline on the protected side. It's bad enough so many people do it on their own without realizing what they are doing, and then have the many problems which flow from that! – Harper - Reinstate Monica Aug 17 at 20:38
1

Ok, but terminology aside, NO you can not use 14awg wires on a 20 amp circuit.

20 amp circuits require 20 amp rated conductors.

If you did not want GFCI protection the line side or wires connecting to the line side could be used to feed the new receptacles. If you do want GFCI protection the load side is used.

You did not state the location of this change; if it is in a garage, unfinished basement, or bathroom, the new receptacles would be required to be GFCI protected.

You can use a 15 amp GFCI on a 20 amp circuit, as that is allowed by NEC 210.21(B)(3).

| improve this answer | |
  • I've added a diagram. All existing outlets are in finished indoor space and the new outlet is outdoors, hence the GFCI. – 0pt1m1z3 Aug 16 at 20:22
  • The pic really doesn’t show the GFCI and everything line side connected because it is not identified. I use line and load because that is code terminology and what professionals use. If you use the load terminals on A GFCI receptacle your new outside receptacle would be protected. it needs an in use or extra duty cover as required by code it would comply with code. So my answer stays the same with the exception of adding the In use or extra duty cover for outside use and tamper resistant receptacle we forget to mention that but it is also a requirement. – Ed Beal Aug 16 at 22:46