5

I'm considering installing an exhaust fan in my bathroom which includes light and heat, and requires a dedicated 20 amp circuit. Would this circuit need GFCI protection? The instructions for the unit don't say anything about it. Even if it's not required, would it be a good idea to do anyway?

3 Answers 3

9

The National Electrical Code (NEC) does not require bathroom exhaust fans to be GFCI protected, however, there is this bit in Article 110.

110.3 Examination, Identification, Installation, and Use of Equipment.
(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.

Which means you have to follow all of the manufacturers instructions while installing the fan. If you read the installation instructions that came with the fan, you might find something like this.

SUITABLE FOR USE OVER TUB OR SHOWER ENCLOSURE WHEN INSTALLED IN A GFCI PROTECTED BRANCH CIRCUIT.
Source

If you install this fan over a tub or shower, the fan must be GFCI protected according to the manufacturer.

6
  • If he has to install it on a dedicated 20 amp circuit then wouldn't running it ahead of a GFI outlet allow for the possibility that one could also plug in other devices to the outlet, like a hair dryer? In this case it is no longer dedicated. Commented Oct 15, 2012 at 15:49
  • @maple_shaft Huh? If it's a dedicated circuit, the GFCI protection would be at the load center. Where would they be plugging in the hair dryer?
    – Tester101
    Commented Oct 15, 2012 at 19:03
  • Breaker -> line -> GFI outlet -> load -> switch -> fan If I plug a hair dryer into that GFI outlet then then the fan is not on a dedicated circuit anymore... or perhaps my understanding of the term dedicated is completely incorrect? Commented Oct 15, 2012 at 19:31
  • @maple_shaft there's no outlet on a dedicated circuit. The diagram is GFCI breaker -> switch -> fan
    – BMitch
    Commented Oct 15, 2012 at 19:33
  • @BMitch Ahhh! I get it. Never seen JUST a GFCI breaker before, thought they only come in outlet form. Thanks Commented Oct 15, 2012 at 19:35
0

needing would depend on your local codes and whether the device has a build-in GFCI breaker

though if the fan needs a ground you probably should add one

however it can't hurt adding one given that a GCFI breaker doesn't cost much

-3

No. GFCI protection is only needed for outlets.

1
  • 3
    Your answer is incorrect. There are certainly circumstances in which devices require GFCI protection.
    – Matthew
    Commented Oct 15, 2012 at 16:26

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.