I am wiring up my kitchen receptacles to have the top outlet on circuit A and the bottom outlet on circuit B. I found this question, which was helpful, but I was flipping through the 2017 Ugly's Residential wiring guide and I saw a section on Box Fill Calculations and I'm really doubting the boxes I'm using are big enough.
My best guess is that I need at least 22.5 cubic inch receptacle boxes, but I'm currently using 18 cubic inch boxes with Wago connectors and pig tails. I do plan to add a receptacle extender to these boxes, since I will be tiling the backsplash, but I don't think that will be enough.
| Item | Unit Volume | Total Volume |
| ---------------------- | --------------- | ------------ |
| 8 conductors | 2.25 ci each | 18.0 ci |
| ? clamp | 2.25 ci each | ? |
| 1 device | 2x 2.25 ci each | 4.5 ci |
| ? grounding conductors | 2.25 ci each | ? |
| ---------------------- | --------------- | ------------ |
| Total | | 22.5+ ci |
I don't think I have a grounding conductor since I'm using PVC boxes, but I'm thinking the Wagos are considered clamps, in which case I'm using 5, so that would be another 11.25 cubic inches, 33.75 ci total. Is that the correct minimum box size required for two 20-amp circuits going to a single duplex outlet? Any suggestions for how to go about this?
Below is a picture of a test box I wired up for reference: