I currently have a 200amp Main panel in my off-grid cabin I am building. I want to feed the panel from my generator which is about 100' in a shed. Originally my contractor a few years back buried cables between the shed and cabin. They are (2) 4/0 and (1) 2/0 cable. I have them terminated in cabin panel. I was wondering if I can put another 200amp panel (or 150amp)in my shed, since the 4/0 and 2/0 are stubbed out in the shed (not connected to anything). I am also assuming that really my "main" panel should be the in the shed, and the "sub" panel in the cabin. My Honeywell generator is a 12kw standby generator, which will supply 50amps I believe. Can I do this?

  • Are you wanting to power anything at all in the shed from the generator? – ThreePhaseEel Jun 17 at 1:30
  • Yes. Probably only a light or two, and an outlet. The cabin is a typically two bedroom cabin, but most power requirements to major appliances (stove, frid, washer/dryer, fireplace) will run off propane, with probably minimal 120v for lights or whatever they use. Biggest thing is my 230v 1 phase pump. Well head is 170' from cabin, and has pump control under cabin in crawlspace. It works fine with my portable generator. – Jon Jun 17 at 1:53
  • How many HP is the well pump, and are the existing wires between the shed and the cabin directly buried, or in conduit? Also, is this Honeywell generator of yours permanently mounted (outside the shed, I hope!) or a portable? – ThreePhaseEel Jun 17 at 2:19
  • The pump has a 4 conductor (3-#8, 1-#10) wires direct buried from well to pump control under cabin. The 4/0 and 2/0 are also direct buried cables. Pump is 1/2 hp. Generator is in shed by itself (10'x8'). – Jon Jun 17 at 2:45
  • 1
    @Jon -- what size is that conduit, and is it plastic or metal? Can you post the photos that you have? – ThreePhaseEel Jun 17 at 23:21
0

It's interesting, the divergence in design philosophies. On one hand, an all-gas cabin (I live in one) has very minimal electrical needs (we have 30A/120V, and what's amazing is I didn't even know that for 15 years, it just never came up until the lost-neutral incident).

So you have this off-grid home that will never have utility power, yet there's a 4/0 service line (not feeder; no ground) suitable for 225A mains service. And no thought toward power at the shed (short of doubling back with another 12/3 UF cable or something).

It's a misfit for the property... like the contractor didn't know what to do, so just did the standard thing for a utility home. The lack of a ground wire is especially eccentric; you have between $500 and $2000 of wire there; overlooking a $40 ground wire seems silly. Since you say it is conduit (is it all the way or just the stub-ups?) you can just add a #4 ground wire of the same metal, and at least solve that.

I would not remain loyal to any of that, since it is so confused. I would re-think the entire thing from the ground up.

A low-key low-dollar DC system

Given the dollar I see already having been put into this, this may a little lowbrow for you: I mention it because from your stated needs, it would suffice.

Given your modest needs, a low voltage 12/24 VDC battery system may suffice. You run an inverter only for loads which are impossible to run on 12/24 DC. For instance lighting is readily available 12/24V. If you look at TVs, DVRs, internet routers etc., many of those have a wall-wart that actually makes 12 volts DC - you can simply bypass the wall-wart and feed them 12V direct. All power conversions are "vampire loads" even when they are in "standby", so avoiding an unnecessary power conversion is always a good idea. However, a refrigerator is a must-have 120V load -- the people who have been doing off-grid for 40 years have determined that it's more cost-effective to upsize the system a bit, eat the conversion losses, and use any modern, common Energy Star fridge - the appliances are so efficient that $3000 bespoke 12/24V fridges can't beat 'em.

Your well pump obviously needs higher voltage AC power due to the long distances both to the wellhead and down the well. (most well pumps are at the bottom). But that inverter only needs to run when you call for water.

You don't need to use cheapie lead-acid batteries that wear out after 5 years, a lithium pack with good on-board energy management is good for 15-20 years. And for 40 year life, they still make traditional Edison Nickel-Iron batteries (which were for EVs; those were popular in the 1900 era when gas engines were really not ready for prime-time).

In this case, the 4/0 might come into play to bring low voltage solar/wind power from an array or windmill, and/or you could store the batteries at the shed instead of the house.

A midrange system

However, a much more comfortable fit would be one of the midrange off-grid systems - not the Tesla PowerWall but vaguely similar options, possibly assembled from various quality subsystems (Morningstar, Schneider etc). In that case you use a quality inverter that does run 24x7 and is able to support all 120V loads... and just go ahead and upsize the system to support that (smaller because quality) vampire load and conversion losses.

For topping up the large battery pack, you can use a generator, but total life-cycle ownership costs will be better on a solar array, windmill or run-of-creek micro-hydro.

If you run the generator, it can be quite small, since it only needs to meet average demand; the battery covers surge demand. Also, you get to run the generator at a time of your choosing, and it runs near full power for the least time possible, which is optimum for both fuel efficiency and wear/tear. The engine isn't running max RPM no load on the off chance that you open a water faucet.

Speaking of that, if you've got the hills for it, think about a tank-up-high to passively pressurize your water system. Then, you only need the pump to top up the tank, and you can do that at a time of your choosing (e.g. when batteries are full and the solar/wind system is in "dump" mode).

In this scenario, the 4/0 would serve little use, except (if you add a ground) to give you the flexibility to put the gen/battery/inverter system anywhere you please. (but I recommend all in the same place).

By the way... if the cable was direct burial and you needed a ground, just saying, Rigid conduit is an allowable ground path and it only requires 6" cover (12" under vehicle pathways). The shell alone covers the ground, leaving you an empty conduit to fit what you please. It's expensive as all getout, but you can trench it with a garden trowel lol.

| improve this answer | |
  • Thanks for long answer. Not sure where or what to do now. Here is the current setting. – Jon Jun 17 at 20:58
  • Thanks for long answer. Not sure where or what to do now. Water is at cabin and I have a 81 gallon diaphragm tank and which currently works with portable generator. So that's good to go. I have to check exactly what's in ground, but I don't think they ran a ground. So simply, generator in shed, gas stub out to shed, cable, trench are all worthless? So I would guesstimate cement pad for outside generator, reroute gas, retrench with new cable, tear out existing cable, and design a workable system. $15 to $20K? MIght as well not bother at that cost. – Jon Jun 17 at 21:04
  • So I guess I have this option. Move the current generator to along side the house on a pad (eliminate shed for this system), and rerun cable that will go from generator into house main panel. Figure out a way to self start it, when pump needs to fill tank, then shut off so it won't dead head the pump. I would assume I would need battery backup to do my minimal voltage draw during the day. – Jon Jun 17 at 21:15
  • @Jon Honestly, I'm guessing that ThreePhaseEel is working on a really good practical answer, that's why I chose to go with a "view from 30,000 feet" answer. Rest assured the cable in the ground can be saved, it's just a question of most expedient and useful method. – Harper - Reinstate Monica Jun 17 at 23:51
  • @Jon -- if you're still with us, can you get us photos of that conduit please? – ThreePhaseEel Jul 17 at 19:56