My house was built 32 years ago, with 200 amp electrical service. Since then I have added a number of large electrical loads, and decided I should do a load calculation for the entire house using NEC Article 220.
Here is what I have so far:
Items I'm unsure about:
Lines 7, 8, 9: Are these square-footages part of my dwelling unit, and thus part of the 3VA/sq-ft calculation? Do they not count at all, because they're not habitable living space? (Lines 7 and 9 are un-heated, and line 8 does not have code-compliant access, an uncompliantly-steep spiral staircase). Does line 9 require a calculation outside the 3VA/sq-ft, since it's served by its own subpanel? It does not, however, have hardwired loads.
Am I counting the EV charger correctly? It is a Clipper Creek HCS-50, rated at 40amps, calls for 50amp breaker & wiring.
Am I counting the water-heaters correctly, do they need to be uprated 125%?
Does 220.53 reduce my total at all?
Anything else that seems wrong (in either direction)?
Part 2 of the question:
If, after corrections given here, I come in over 200 amperes, how worried should I be?
If I decide to upgrade my service to 225 amperes, what is required other than a 225 ampere main load center?
- Obviously, and cheaply, the THW cables from the meter to the main breaker (currently 2/0 for hots and 1/0 for neutral).
- What about the transformer (I have my own private one in this rural area), the lengthy buried cables from the transformer to the meter base, and the meter itself?
- Are these questions only the POCO can answer?
- Call to them said surely the transformer/cables/meter can handle 225 amps; pinned down, they said cables were 4/0 aluminum (3/0 neutral) which ampacity charts seem to say are only good for 180 amperes; so something doesn't jibe.