New here! I am DIYER who rehabs homes and rents them.

I’ve worked with a few panels but never came across one like this, which seems like a split bus panel.

It seems I didn’t adhere to the 6 breaker rule, I believe that’s what it is called and added some of my lighting and outlets on the first 6 spaces.

I guess my question would be should I remove those 4 breakers and place them below the red circled double pole breaker? I imagine that breaker will activate or deactivate any power below it, but not above it.

Also, if I were to use the the first 6 slots, what are they exactly used for and is there anyway to kill the power to those slots without having the meter pulled?

Thanks!!

enter image description here

8
  • Can you provide us with photos of this panel's labeling? (especially the label on the inside left) Commented Jun 8, 2020 at 16:16
  • I find it hard to believe that there isn't a breaker/fuse outside, at the main disconnect.
    – Hot Licks
    Commented Jun 8, 2020 at 22:52
  • @HotLicks Most of my neighborhood was built with panels like this (though a different brand) - they have no main breaker or fuse (inside or outside). Instead they have 12 spaces at the top meant for 6 double pole breakers, one of which feeds the lower half of the panel. Since all power can be turned off with six motions, it is still code compliant.
    – Moshe Katz
    Commented Jun 9, 2020 at 13:06
  • @MosheKatz - Certainly wouldn't code here -- an outside cutoff is required.
    – Hot Licks
    Commented Jun 9, 2020 at 13:08
  • @HotLicks It wouldn't code here today either, but this neighborhood was built in the 1970s so existing units remain compliant.
    – Moshe Katz
    Commented Jun 9, 2020 at 13:16

3 Answers 3

5

The origin of Split-Bus panels

So, think 1920. Lighting is the "killer app" that is making everyone electrify their homes. Plug-in appliances are still coming along, but by and large 30A is plenty for most people just doing lighting and the few plug-in appliances of the day, with 60A for those with a big electric appliance.

Now, think 1950. Postwar, they're building houses like crazy, and they have new-fangled "all electric" appliances - electric ranges, electric dryers, electric water heaters - some houses even have electric heat! And why not? Nuclear fission plants are in the pipeline, and just around the corner is nuclear fusion -- clean, safe and too cheap to meter. The old 30A service (for mainly lights) or 60A service (for lights and maybe one big electric appliance) just doesn't cut it anymore.

The problem is, service equipment hasn't been keeping pace. Miniature circuit breakers exist, but the design mentality is still stuck in 1920 - with 60A being the largest main breaker that's really made in any production. And these new homes need at least 100A, and 100A main breakers are nosebleed-expensive industrial tier products.

"Well", say builders. "How about if we split the main breaker function to several several affordable main breakers? You have to throw them all to de-energize the house. Figuring on electric range, dryer, water heater, A/C, and a fifth to feed an internal 'subpanel' for traditional 'lighting' and recep loads". And the panel builders said "It needs to be an even number." And NFPA said "alright, six it is. You must be able to turn the power off with 6 hand movements". Which also happens to be a rule in industrial power.

And so they built in the panel with a "built-in subpanel" for "lighting" (read: normal 120/240V loads).

So the top 12 spaces, the "Rule of Six" area, are for major (electrical) appliances that pull 240V. Thus the 6 need 12 spaces. You can put single-pole or even double-stuff breakers in there, but you won't be able to use all 12 spaces if you do.

Is the panel legal as pictured?

I count 1-2-3-4-5 throws. Yes, you can do that and put 1 more breaker in the Rule of Six area. However then you are done. You may find that stifling, so I recommend putting small loads in the subpanel area.

It also remains that Rule of Six/split-bus panels are scary dangerous, because if you have 50A range + 30A AC + 30A water + 30A dryer + 60A for the lighting section + a 100A breaker to the Tesla charger, you may notice that's 300A of "main breakers" on a 125A service. As houses power more stuff, you have a higher chance of blowing right past the safety limits on the panel - and nothing catches this on a split-bus panel!

Meanwhile 100A and larger breakers have come down massively in price. So I like to see Rule of Six panels converted into "Rule of One" panels one of several ways:

  • Given that exterior disconnects are Code requirements in 2020, fit an exterior main breaker and put the Rule of Six panel downstream of it. Now it's just another panel, and you can continue it in service forever. (and your CH panel is excellent and you have every reason to do so).
  • Fit a single breaker into the Rule of Six area, and have that power a new subpanel. Now you have a single breaker shutoff.
2

The way your setup is is the top section is always hot. I normally use the upper section for powering the lower section, as well as the electric range , and other large draw devices or sub panels.

Most of the homes built in this era do not have main breakers at the panel. As new codes are implemented or updates to the systems this is being required.

For now the only way may be to have the meter pulled to remove power to the top section.

2

There is a few funny things happening in this panel.

First, you are correct it is a split bus panel but it is not being used as a split bus panel. The only breakers I see in the panel are the 4 branch circuits actually being used as main breakers, and the one main breaker feeding the area that is supposed to be for branch circuits. So those breakers need to be moved down into their proper location.

Second, this panel has a dedicated grounding bus, on the left. Which seems to indicate that it is a subpanel and not a main. Is there a main breaker at the meter or a main panel ahead of this panel?

Third, the panel is being fed with a two wire shielded SE type cable. Meaning the shield which is primarily used as a ground is connected to and is attached to the neutral bus and being used as the neutral.

Fourth, I see a grounding electrode conductor coming in from the right side and also connecting to the neutral bus, and I don't see a bonding screw to the panel. This means the grounding bus is isolated and serving no purpose or at least it is installed incorrectly.

Needles to say this panel was not installed by a professional and was probably never inspected. If my assumptions are right this panel presents a shock hazard for any one working on it or any circuit down stream of it.

My best advice is to uninstall this panel and the feeder and install it properly according to your jurisdictions codes. At the very least you need to correct your grounding and neutral bus buy moving the grounding electrode to you grounding bus and bond you neutral bus since you have no effective grounding electrode coming from upstream. This still doesn't make it legal and I do not recommend it for a permanent fix, but it would help protect you from electric shock.

When considering your options of a cheap bandage or a more expensive proper installation, keep in mind that this panel is a hazard and a human life is at stake.

Good luck and stay safe.

4
  • 1
    Actually, the GEC is supposed to land on the neutral bus, see 250.24(A)(1) Commented Jun 8, 2020 at 16:13
  • Hi Master Elec, thank you for your answer! There is no shutoff before the panel. I added the ground bar to the panel and screwed it in using the two provided screws. I then took one of the ground lines from the right and spliced it and carried it to the grounding bar I added, thinking this would make for an effective ground, per a friends rec. This panel has it own meter and line for 2nd floor unit. If I removed the bar I added on left and added the ground to the gold screws on the right bar and the neutrals below on the silver screws would that be correct? This is how it was prior. Thanks!
    – Al K
    Commented Jun 8, 2020 at 17:03
  • @ThreePhaseEel - Only if it is a main panel. Commented Jun 9, 2020 at 12:41
  • @RetiredMasterElectrician -- indeed, I'm presuming it's a main panel because of the 3-wire SEU feed and the lack of a shutoff upstream Commented Jun 9, 2020 at 12:47