Adding 1 extra light total of 2 on circuit. Need to know what gauge of copper wire to add to aluminum 12-2 gauge 3’ span.
I will use AlumiConn connectors
You'll want 14/2 NM...
The rule for converting between aluminum and copper wire gauges is that in order to carry a given amount of current, you need an aluminum wire two sizes larger than the copper wire you would have used. So, a 12AWG aluminum wire is rated for the same 15A as a 14AWG copper wire is, and NM is apropos since jurisdictions that don't permit NM also generally don't permit the use of aluminum, especially at branch-circuit gauges.
...and a torque screwdriver
While your choice of AlumiConns for this job is a good one, as they are the most reliable way of making an aluminum-to-copper branch circuit wiring connection available to the rest of us, they, like all mechanical setscrew splice/tap connectors, are sensitive to tightening torque. As a result, a using an inch-pound torque screwdriver to tighten the connector screws to the manufacturer's specified torque value is highly recommended for long-term reliable results.
(Sidenote: if you're having trouble with the relatively chunky Alumiconns taking up too much room in the box, get a Wiremold ceiling starter box and use it as an extension ring to add extra volume.)
  • C'mon upvoters, this is a good answer! – Harper - Reinstate Monica Jun 6 '20 at 6:11
  • Just as an FYI, they do have a non-torque method too (quarter turn past resistance, if memory serves), but the torque is preferred. I bought a torque screwdriver to do mine (I still work with them from time to time in my house) and it was prohibitively expensive for a one-off project. – Machavity Jun 7 '20 at 14:57
The rules for the minimum size wire allowed are determined by the size of the overcurrent protection (i.e. the breaker or fuse). The maximum overcurrent protection allowed for #12 aluminum is 15A, the minimum size copper for 15A is #14. You can use larger than #14 if convenient, but must use the size of overcurrent protection that matches lowest rated wire in the circuit.