2

I am trying to troubleshoot an issue. All outlets downstream from my GFCI will not work when I plug anything in. with my DMM I pulled the GFCI from the wall and measured voltage into the GFCI from Hot to Ground = 120 Neutral to ground = .5 Neutral to hot 120. Out from the GFCI Hot to Ground = 120 Neutral to ground = .5 Neutral to hot 120. I go to the next outlet and I get Hot to ground 120. Neutral to ground 1.5 Hot to Neutral 112v. any ideas on how to resolve? When I trip the GFCI all reading on the outlet goes to almost 0 as would be expected. It is important to note I have replace the outlet not working to no avail. I get the same readings without an outlet attached

1 Answer 1

2

Loose neutral on either the GFCI, the socket under test, or an intermediate socket.

1
  • 1
    Yep, classic loose or high resistance neutral connection somewhere.
    – JRaef
    Jun 3, 2020 at 21:47