boxI've bought a timer switch for my bathroom that requires a neutral wire.

On opening the switch box, I see a white wire screwed to a copper ground that is screwed to the back of the box.

Is that my neutral wire?

The other wires are black (hot/in, split between the two switches), gray (load to lights from the right switch), and white (load to fan from left switch).

Thanks in advance!

2
  • Oh, that's not good. That indicates there was a pre-existing problem in this box before you even got there. Are any of these switches 3-way? Powered switches by chance? By the way, can you settle for a plain old twist style timer or are you married to the touch-buttons timer? – Harper - Reinstate Monica May 9 '20 at 20:16
  • @Harper-ReinstateMonica Yeah I think that's totally a hazard- both wires in the romex on right are runners, and that must mean there's a copper ground wire being used as return- which is tied to neutral and box. Accident waiting to happen. Or even worse. – J.Hirsch May 10 '20 at 15:22
2

Edit at the top:

OK I got a better look at your wiring and I see what they did (party foul!). And I'm going to 'upgrade' my... this isn't good.

The feeder circuit is on the left. Incoming hot and neutral. They didn't run a 3 wire run on the right, so they stole the white wire (neutral) and made it another hot runner. That makes the wires on the right going out 'runner 1' and 'runner 2'. One of them runs to your fan, and one of them runs to your light.

Unfortunately, there is no return path for the electricity. You said there's copper coming into the box- which I can't see from the wires- so my guess is they stole the bare copper wire to become your return path. Had they run a 3 wire (Black, Red, White, copper-ground) they'd only need one wire path.

I hacked together an image. I suck at mousing, laughter should help ease the pain.

On the left you can see a white wire coming off the switch and going up into the romex on the right (runner 1)- that is now carrying power. The party foul here is it should be labeled - either with a black sharpie (color the end) so people know it's hot, or wrapped with some black electrical tape. I mean, it is sort of obvious, but I believe code calls it out anyway.

On the right you can see a black wire coming off and traveling up into the romex on the right. That's also carrying power, so it's 'runner 2'.

So your switch box itself is being used to tie ground and neutral together.

Since you said this is in the bathroom... I'll be honest with you- this is REALLY dangerous. Like... get yourself or your family killed dangerous. Assuming it's within 6' (2 meters) of a sink with water, you could theoretically provide a very good path for electricity to make it to the water and electrify yourself IF something else goes wrong.

Reason being is that whole box is carrying power. It's hard to see from just the one photo but I don't think I'm missing something.

Now, what to do:

You can sort-of fix this. But maybe just not in the way you'd like. Simply put you don't have enough wires going out of the box to feed the fan and light. Now interestingly there are a couple of solutions that might work but that would entail fixing/modifying the fan.

I assume the fan and light are integrated into a single unit?

The easiest and safest thing to do to day without bringing in an electrician is to disconnect the switch/timer for the fan, and wire the fan and light together. That means when the switch comes on, the light and fan turn on at the same time. I know this is NOT what you want, but it would be a temporary fix until you can have someone come run a 14/3 wire up the wall and into the fixture.

If this is going to be OK, let me know, and I'll write up some more detailed instructions.

If you can take some more enter image description herephotos too showing copper lines I'll try and think of how else it might be wired.


So that's really not good to see. I tried to visually trace your grounding, and it appears that the ground comes from the metal box to the outlet on the right, then over to the one on the left. And at no point do I see it go anywhere else.

So with that, no, your box is not wired right, and more importantly... it's a hazard because your 'neutral' which is your 'return path' for electricity is hooked to the metal ground box. It goes hot, you go hot.

I also don't see any bare copper coming into the box from anywhere. If it is there and you take a photo that'll help.

So first things first, and I'm a bit uncomfortable saying this, you ought to find someone that can give that a good look and test things before you disconnect it.. but I'd get that bare copper wire and your neutral white broken apart.

Then you could use that neutral, assuming it's not wired even funnier than the box.

Can you describe more of what the switches do? I assume that one is an outlet, the other is a switch- thus power (and neutral) coming in are feeders, then the line going out is broken at the switch, and the neutral coming back from that is tied into the neutral going out with the feeder.

4
  • Wow. Thank you so much for the responses. 1) the left switch is a two-way on/off for the bathroom fan. The right switch is a two-way on/off for the bathroom light. 2) there is copper coming to the box, it's just obscured in the photo. 3) yes I could go with a twist-timer, but don't like the idea of leaving a messed up situation in the box... – GFab May 9 '20 at 21:19
  • 1
    And 4) How bad a hazard is this setup? With Covid, I really want to avoid electricians if possible, but definitely also want to avoid worse stuff like fires! – GFab May 9 '20 at 21:25
  • Give me a couple minutes coming dinner – J.Hirsch May 9 '20 at 21:26
  • 1
    Wait, is there additional lines coming in on the right side bottom? Can you get some photos with the lines coming in and out more clear? It's not a bad setup, it's just not right (at least). The reason code is written the way it is is that bad things have happened and it's cost lives- so doing it right is sort of paramount. With switches, what electricians do is run just a single wire up/and return- so you could have two hot's out (switched) and a single wire coming back. But that should be labeled. Just need to see better. – J.Hirsch May 10 '20 at 1:07