Goal: Understanding the NEC code language for practical DIY application.
All occurrences of the phrase "no other outlets" related to a house (not an RV) in the NEC 2017 are:
210.11 Branch Circuits Required.
...(C) Dwelling Units.
...(1) Small-Appliance Branch Circuits. In addition to the number of branch circuits required by other parts of this section, two or more 20-ampere small-appliance branch circuits shall be provided for all receptacle outlets specified by 210.52(B).
...(2) Laundry Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.
...(3) Bathroom Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one 120-volt, 20-ampere branch circuit shall be provided to supply the bathroom(s) receptacle outlet(s). Such circuits shall have no other outlets.
...(4) Garage Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one 120-volt, 20-ampere branch circuit shall be installed to supply receptacle outlets in attached garages and in detached garages with electric power. This circuit shall have no other outlets.
210.52 Dwelling Unit Receptacle Outlets. This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. [...]
...(A) General Provisions. In every kitchen, family room, dining room, living room, parlor, library, den, sunroom, bedroom, recreation room, or similar room or area of dwelling units, receptacle outlets shall be installed in accordance with the general provisions specified in 210.52(A)(1) through (A)(4) [about spacing etc].
...(B) Small Appliances.
...(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
...(2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets.
625.40 Electric Vehicle Branch Circuit. Each outlet installed for the purpose of charging electric vehicles shall be supplied by an individual branch circuit. Each circuit shall have no other outlets.
These texts confuse me: 210.52(B)(2) applies to the branch circuits of 210.52(B)(1). In turn, 210.52(B)(1) initially includes (something like) only food-related areas, but then extends to receptacle outlets covered by 210.52(A), which includes almost the whole house including the mentioned food areas except, roughly, the pantry and breakfast room.
Questions:
- Why is it written like this? What is the intent?
- To which spaces/areas does the "No Other Outlet" of 210.52(B)(2) requirement apply?
Example dilemma:
Let's take a new bedroom:
Interpretation 1: This bedroom, INcluding all of its wall receptacle outlets, is covered in 210.52(A). Hence, 210.52(B)(1), by referring to 210.52(A), does require all bedroom wall receptacles to be served by one or more "20A small appliance branch circuits". So no other outlets are allowed.
Interpretation 2: This bedroom, EXcluding all of its wall receptacle outlets, is covered in 210.52(A) (so just the abstract room space; its receptacle outlets are not explicitly mentioned). Hence, 210.52(B)(1), by referring to 210.52(A), does not require all bedroom wall receptacles to be served by one or more "20A small appliance branch circuits". So other outlets are allowed.
Which interpretation is correct?