I have a bathroom outlet where the GFCI is going bad and needs replacement.

There is one line and 2 cables coming in for 2 loads so there are 3 black wires, 3 white wires, and 3 ground wires coming into the box. One of the loads goes to the overhead light switch and the other goes to the light switch in another bathroom.

When I rewired the new one exactly as the old one it wouldn't work. The green light on the GFCI would come on for a brief second and then go off, and the circuit breaker seemed to be making a quick buzz sound as soon as it was thrown on.

I know I have it wired correctly in terms of the line and the load positions. From previous posts I read I'm wondering if the problem is with the multiple ground wires tripping things. The old GFCI had all 3 ground wires connected to the screw on the bottom.

If this is the problem what is the best way to wire this outlet?

4
  • 1
    Can you post photos of the inside of the box please? Also, is there a reason you want the bathroom lights GFCI-protected? Mar 30, 2020 at 2:39
  • No, this is just how it was wired. I think I figured out that the fan in the bathroom, and not the lights in the neighboring bathroom, is the other load wire.
    – Terry Rex
    Mar 30, 2020 at 3:01
  • There's no reason to put fan and lights on LOAD unless they are inside the shower. In any case, the first step to troubleshooting a GFCI is removing everything from LOAD. Mar 30, 2020 at 3:24
  • So then how do I power them (the light and fan)?
    – Terry Rex
    Mar 30, 2020 at 3:41

1 Answer 1

5

I think I know the problem...

It's not necessary to put GFCI on a fan or light unless it is in the shower.

The LOAD terminals are not for onward power to other points-of-use. The LINE terminals are for that. Any GFCI is capable of protecting onward points-of-use; when you actually want that, you put it on LOAD.

It sounds like the last guy put both this light and the other bathroom's light on GFCI either out of ignorance or "because it's saferer".

I do believe that "saferer" has paid off. One of the lights or the wiring has a ground fault.

I gather this never occurred to you, but it all adds up. The old GFCI didn't trip because it was bad; it was doing its actual job. You replaced it, and the new one also tripped because it was doing its job.

How to test or replace a GFCI so that doesn't happen

First, if a GFCI refuses to not trip, you must remove everything from the LOAD wires before you can meaningfully test it. Obviously if you remove a downline from the LOAD terminals and suddenly the GFCI behaves properly, the removed downline has a ground fault.

So that is one way to solve it: work the problem.

The other way is simply move the faulting load to the LINE wires and not worry about it... but that seems reckless. It's one thing to not bother to GFCI protect things that don't need it. But a whole 'nother thing to ignore a problem you know is there. I mean if you did, and then a fire started there... you'd feel pretty dumb.

2
  • So can I just cap the 2 load cables that are coming into the box (one for the light and one for the fan - not in a shower) and just connect the line wires? I want to replace the existing gfci because it's showing signs of wearing out by the buzzing sound it makes when something is plugged in and turned on (like a curling iron) and there is a slight bit of scorching (light brown) on one of the plug slots.
    – Terry Rex
    Mar 30, 2020 at 21:59
  • @TerryRex -- unless the fan's in the space directly over the bathtub, you simply can nut all the hots together, all the neutrals together, and all the grounds together, including pigtails, then wire the GFCI's LINE terminals to those pigtails Mar 30, 2020 at 23:48