I bought a house about a year ago and I have an old Cutler-Hammer electrical panel. I see the number 2001 written on there, but no idea when it was installed. I have a few questions about this panel:

  1. When should a panel be replaced?
  2. Should I have any concern that this panel is Cutler-Hammer (which is no longer in business, but was purchased by Eaton)?
  3. I cant tell what breakers were installed, but they don't seem to all be cutler hammer. Should I be worried that they seem to be different brands?
  4. I would like to replace most of these breakers with Dual GFCI/AFCI (because old house, little kids). Would this be the right breaker (Eaton) for this panel?

Cutler-Hammer label Breakers Some breaker labels

  • 3
    dont have much time so just a comment, you never have to replace a panel because of age , cutler hammer is available through Eaton not out of business but merged , As far as the square D breakers in your panel I think that is a problem but as far as the panel and breakers they are fine, just don’t think HOM are listed for use in a CH panel but will look when I have more time. – Ed Beal Mar 9 at 22:03
  • If it helps, those breakers are Square D. – TomC Mar 11 at 15:39
24
  1. Not in your lifetime.
  2. Nah, it's cool. Eaton has owned Cutler Hammer since 1978.
  3. Alien breakers require immediate attention!
  4. BRLAFGF115 and BRLAFGF120 are fine.

This looks like a Cutler Hammer "BR" 40-space panel that is full.

The panel is perfect.

Mergers & acquisitions are normal in that business. Eaton just chose to acquire Cutler-Hammer, instead of develop their own line of electrical equipment from scratch with zero experience and blundering into every possible mistake. It's the same model numbers, same tooling, same factories, same everything. The only real difference is Eaton's logo is cooler.

This kind of panel lineage is normal; your panel actually harkens back to Westinghouse, Challenger, Bryant (hence BR), Cutler Hammer and now Eaton. Indeed, your correct BR breakers are UL cross-listed type C for Challenger.

I am a CH fanboy, but I will concede a couple of advantages to BR. First, BR breakers are better supported, like their line of remote-control breakers nobody else has; like the BRRP and BRRSP (for BR panels) and nothing for CH. Second, anything Eaton does in their CH line, they can also do in their BR line, because BR breakers are wider; they can just put CH guts in BR bodies.

Eaton is also a specialist in making UL-Classified breakers for competitor panels; these require a tortuous UL-approval process to prove compatibility with the shape of the bus stabs on competitor panels, and Cutler Hammer mastered that to the satisfaction of UL, with their CL line, which is listed for several competitor panels. You'll soon see why I mention this.

However, it's full of alien breakers

Which means you'll have a lot of Siemens/Murray QP, and Square D HOMeline breakers to sell on Craigslist. None of those are UL-classified for this panel.

There's a myth, believed by some handymen, that any 1" breaker is compatible with any other. I wrote that last paragraph to explain why that's a lie. Honestly I wouldn't be surprised if a couple of your bus stabs are burned, because that's what happens. That makes the space unusable. Fill the hole with any breaker painted red. (I don't like using factory hole-filler kits because I find them flimsy).

A few breakers in there are so old that they can't be identified by front markings. If they're BRyant or Cutler-Hammer, they are fine. However if they are Challenger or Westinghouse, into the trash they go. Westinghouse is just too old. Challenger was swept up in the scandal with FPE and Zinsco breaker safety, but unlike them, that only affected Challenger breakers; Challenger panels are safe as houses if you change the breakers to C/BR.

The right breakers for your panel

Absolutely nothing on Amazon is the right breaker for your panel. Amazon is inundated by third-party sellers, who sell counterfeits or straight junk off Alibaba. Most people buying from Amazon don't even realize they're buying from the Amazon Marketplace flea market, which is the same quality tier as eBay.

Further, mail order generally for electrical equipment is a terrible idea, because equipment is generally of low cost and high weight, and that means shipping is prohibitive - and yeah, you pay for shipping one way or the other. Price-check both local big-box stores and 2-3 local Electrical Supply Houses; big-box usually tries to be lowest on endcap high-mover items like 14/2 cable, but on most other things, a good electrical supply is the best price. I just stopped buying at Home Depot after finding they are too expensive on most things. Keep in mind not every Electrical Supply is actually an Eaton dealer.

All that said, the only breaker type listed or classified for your panel is Eaton Type BR (which is cross-listed Type C). Eaton keeps prices low, which is why there are no classified options. You're looking at $4.50 a breaker, unless you get up into AFCI or GFCI.

You have one CAFCI (Combination Arc Fault Circuit Interruptor) breaker in there right now. A CAFCI means it looks for two types of arc faults: series (bad connection) and shorting (wire sparking to ground). The latter provides a weak GFCI protection - too weak for human safety. I assume the choice of CAFCI for a jacuzzi was made by the same mouth-breather who specced all those alien breakers. That's OK, it can be moved to a bedroom.

For places likely to be wet, dual-mode AFCI+GFCI breakers are ideal, so they confer GFCI protection to the wiring as well as the appliances. However for receptacles that have no risk of being inundated with water, it's perfectly fine to use an AFCI-only breaker like that one, and then a GFCI receptacle at the first outlet, feeding the rest of the circuit from its LOAD terminals.

However, it's full.

Well, I see a few breakers that seem to go to nothing. I also see a whole-house surge suppressor that could easily be combined with something else on a 30A breaker, the A/C at the top right would be an ideal candidate since its position and sizing are correct.

So before you run out of space for normal sized breakers (note GFCI/AFCI don't come in double-stuff), start thinking about where a subpanel would make sense. BR, of course, unless you want a generator interlock on that subpanel, then Siemens/Murray because they make a suitable $23 interlock kit (Eaton doesn't, and can't use QP breakers in BR). One thing we learned about generator interlocks is you really, really want GFCI and AFCI breakers to be after the interlock.

| improve this answer | |
  • 3
    Try a few AFCI’s prior to jumping in with both feet. I support AFCI’s for bedrooms but they have trouble with solid state lighting circuits especially heavily loaded dimmers, motor control with AFCI is a headache refrigerator, freezer, washer dryer, garbage disposal, vacuum cleaners, hair dryers are just a few of the items that AFCI’s have problems with. Like you I have been asked to swap out to these safer breakers. Every time I am back after warning the owner with the same list, and once used you can’t return them at 30 bucks a ea just do your bedrooms that’s where AFCI’s were first Required – Ed Beal Mar 9 at 23:10
  • 3
    Amazon Marketplace is substantially inferior to eBay, since with eBay you purchase from an identified seller, and Amazon dumps all of its supply into a giant bucket, and you might get a counterfeit even when "buying" from the manufacturer itself. – chrylis -cautiouslyoptimistic- Mar 10 at 20:40
  • 2
    @hobbs the allegations I hear a lot is that Amazon (or workers?) will cheerfully substitute a seller X item for a seller Y item if seller X claims it is the same SKU/UPC. Perhaps Seller Y authorizes this, which is a real problem if Seller Y is Amazon. It may just be workers doing the substitution ad-hoc, e.g. when the computer says an item is in stock when it's not, effectively kicking the problem down the road. – Harper - Reinstate Monica Mar 10 at 22:24
  • 3
    @hobbs Fulfilled by Amazon (which is nearly everything on the Marketplace) mixes inventory from multiple sellers into a common stream. – chrylis -cautiouslyoptimistic- Mar 11 at 0:57
  • 4
    @chrylis also here Real horrorshow, the knockoff makers can just barge right in, and Amazon does not apply common sense. – Harper - Reinstate Monica Mar 11 at 1:30
9

Panels normally get replaced because more breakers are needed than are available in the existing panel or the total load requirements exceed the panel rating. Panels can also be replaced because the existing panel manufacturers have a history of inferior, unsafe products. You do not need to replace yours.

Cutler Hammer makes great panels and Eaton has kept the quality standards high.

You have a smorgasbord of breakers in that panel and from what I can read, a number of them are alien breakers. While these probably have preformed well in the past, they should be replaced.

Eaton does make a dual GFCI/AFCI BR breaker that will fit in this panel. They go for about $45 bucks. Do not buy them on Amazon. Get them from an electrical supply company.

There are some real experts on this site that will do a great job of spelling everything out in great details. Wait for them to chime in.