7

First, thanks to all the users who take the time to respond to all the questions on here. I've learned so much over the years but this is my first post/question.

I'm wanting to replace my ~15yr old GE electric cooktop with a GE induction one. I took a peek at the current wiring in the box and I'm curious your thoughts. The previous owner of the house seemed to pull permits for any work ever completed so I can't imagine this was done incorrectly/unsafe, but I also can't be sure. My guess is that they had the appliance store do the install.

House was built in the late 80's and has stranded alu wiring coming into the junction box for the cooktop. Sounds like this common(?) for appliances like cooktops and stoves. The cooktop and downdraft has copper wire, and as you can see, everything is wire-nutted together. First question - is that okay? I've read articles ad nauseam about alu/cu but so much of it has to do with single strand aluminum wiring. There might have been some sort of ox-gard applied as there's a trace of sticky residue under the nuts.

Next question - if you look at my annotations below, the white wire from the downdraft is wire-nutted with the ground from the cooktop and circuit. Is that weird? Correct?

Everything has been like this for 15yrs but I'm not saying that makes it okay. Since the new induction cooktop has the exact same 3-wires as my current (old) one pictured below (and they're both 30a), the easy thing to do would be reinstall as it currently is (assuming it was done correctly) and coat everything in ox-gard.

Thanks for any input!

cooktopwiring

4 Answers 4

5

Aluminum that was used 15 years ago is not a problem (old AA-1350 Alloy vs new AA-8000), but those wire connectors aren't listed for aluminum. Most twist on connectors for aluminum won't properly accept that size of wire, typically you need a set screw style connector.

1
  • Thanks! That's just what I was wondering about the aluminum. Though the house (and presumably it's wiring) was from 30yrs ago. It's the cooktop that's 15yrs old.
    – Eric24v
    Commented Mar 3, 2020 at 19:21
5

Legacy neutral (not ground)

Yes, this is kind of a big mess, because it's a 3-wire connection (hot-hot-neutral) with neutral masquerading as ground. It is not ground. It is neutral.

Normally that's illegal, even in 1980, but you see how the neutral wire is a disorganized bunch of strands field-twisted together? That actually makes it leeeegal. That's SE cable, and the neutral becomes a web that surrounds the other two conductors. It's a service cable, so it's neutral not ground. You were never allowed to use /2 w/ground cable, because you could have as easily used /3 w/ground. I suspect that rule was to allow the supply chain to use up their stock of 40A SE which has little other use, since 40A services are outlawed.

So, the hood tapping the bare aluminum for neutral, is actually fair game. It is neutral. The problem is that the range hood is also bootlegging ground off this neutral. That is not allowed, unless you are a range. Or to be more precise, the range is allowed to make a 3-wire hot-hot-neutral connection, and then internally attach the range chassis to neutral with a jumper.

This 3-wire range connection still isn't a good idea. If that neutral wire breaks, it will electrify the chassis of the range. As wired, it will also electrify the chassis of the range hood.

Retrofit ground

Honestly, if this were me, I would do one of two things for sure: Either a) put a GFCI on this supply circuit, or b) retrofit ground. Or both.

I would fastidiously insulate the webbed neutral wire coming off that SE cable, so it is entirely insulated from the faux grounding of the steel junction box. I'd use tape and heat shrink tubing, and for style points I'd go with white or gray shrink tubing; the inspector will like that a lot.

Then, I would run a #10 bare ground wire from the ground lug on this junction box, back to any of a) the panel, b) any grounded 30A+ circuits going back to the panel; c) any non-flexible conduit going back to the panel; or d) any part of the panel's Grounding Electrode System, i.e. the copper wires heading off to water pipes or ground rods. Not water pipes directly.

Then, I would make a 4-wire connection to that range, removing the range's N-G jumper, and grounding everything to those steel junction boxes. This ground retrofit will provide the best safety; I'd rank it slightly above a GFCI for safety.

The conversion of the SE cable's neutral wire to an, um, neutral... is perfectly legit, because it's SE cable and that is neutral. The fastidious insulation of it is vital to ground doing its job.

If you do not retrofit ground, then it becomes vital to fit a 2-pole GFCI breaker. This will be an expensive piece, but it protects you from a common and lethal failure mode of 3-wire-connected ranges and dryers.

Splicing aluminum is a big deal, though.

As NoSparksPlease points out, those splices won't cut the mustard. The aluminum wire is too big for Alumiconns.

So you will need to get appropriate Polaris style connectors to make the splices between the AL conductors (H-H-N) and the range and hood. That is a deep 4" square box, but it's still going to get very full very fast.

One trick is to get an accessory ground bar intended for a service panel, and hack it up to give the number of voids you need (1 per wire). But then it must be fastidiously insulated with electrical tape; that's hard to get right, and inspectors dislike it because they can't inspect a wad of electrical tape.

That range hood

First, wiring that range hood into the range circuit is definitely illegal unless you retrofit a ground, because the range hood needs a real ground. However, I don't believe it can share the range circuit unless you get a variance from your local inspector. (who supposedly inspected and signed off on this, yes?)

Nor can it share a kitchen countertop receptacle circuit, unless again you get a variance.

5
  • I thought the only place a neutral could be bare was in the service drop and that after that it had to be insulated. Seems like a stretch to call that a neutral.
    – JACK
    Commented Mar 3, 2020 at 21:21
  • 1
    @JACK Your logic totally makes sense in a post-grounding world. The use of SE cable for dryers and ranges is an artifact of the pre-grounding age; it's not ground at all. It's neutral only. That is obfuscated here, because of the metal boxes and the way the hood bootlegs ground. Commented Mar 3, 2020 at 22:14
  • That how I wired up my H.S. graduation present... a welder. That was in the mid 60's... not late 80's.
    – JACK
    Commented Mar 3, 2020 at 23:19
  • @Harper thank you for taking the time. If you’re ever in Bellingham, WA I’ll buy you a beverage of your choice. And if you know any trustworthy people to tackle this the correct way, let me know and I’ll hire them (the style points are especially important, ha!). Obviously some dingbat did this the wrong way despite being apparently qualified to do it correctly.
    – Eric24v
    Commented Mar 4, 2020 at 18:43
  • @Eric24v Thanks. It's possible the inspector was old-fashioned and decided to approve it anyway, setting aside the reasons NEC prohibits it. The range circuit, alone, would be grandfathered. Commented Mar 4, 2020 at 19:04
3

The two hot legs and ground from the source are OK for the cooktop because it's straight 240 Volts and the neutral isn't needed. Unfortunately, the neutral is needed for the downdraft and using the ground to complete that circuit is a big NO NO! The downdraft should be on a different circuit with a neutral and properly protected by a breaker sized for it's load and not by the breaker for the cooktop. That, along with the wire nut problem, should be fixed.

4
  • What about regular wire connectors packed with Ox-Gard? Are the purple al/cu ones special beyond being packed with anti-ox? Higher temp plastic maybe?
    – Eric24v
    Commented Mar 3, 2020 at 19:34
  • Argh, that's what I presumed about about the neutral on the downdraft after hours of reading last night, and that's what ultimately led me to post the question here. Since this seems to happen frequently, what is the only plausible explanation for someone doing it that way? And, what's the potential impact? This has me concerned enough to go unwire the downdraft completely.
    – Eric24v
    Commented Mar 3, 2020 at 19:51
  • @Eric24v OK Here's where we have some problems. There are some wire nuts "approved" for aluminum but they have failed with disastrous results so no one uses them. Alumiconn makes a good connector to the best of my knowledge.
    – JACK
    Commented Mar 3, 2020 at 20:13
  • Hopefully, Harper, Ed or threephase will chime in.
    – JACK
    Commented Mar 3, 2020 at 20:22
1

NoSparksPlease is right. There are two issues with copper to aluminum electrical connections. (1) current passing through a wire produces heat. Heat causes metal to expand. Copper and aluminum expand at different rates causing ordinary wire nuts to loosen resulting in a fire hazard. (2) Combining two different metals such as copper and aluminum in an electrical connection also results in a galvanic response (oxidation/corrosion) which weakens the wire with the same potential result - a loose/broken wire.
You need to make sure you are using an approved connector for this. One that I prefer to use is AlumiConn which has an anti-oxidant paste and torque screws. Torque is usually 15-20 psi. There are a few others as indicated above. However regular wire nuts with anti-oxidants in them won't cut it. They only solve half of the problem.

3
  • Right - I was giving background on the copper to aluminum discussion. The only other approved connector is Copalum which can take larger gauges than Alumiconn and is approved for stranded copper. Don't think it's approved for stranded aluminum as yet but you can check it out. I would follow Harpers guidance on getting a proper ground.
    – HoneyDo
    Commented Mar 4, 2020 at 19:45
  • Both Alumiconns and COPALUM are limited to 10AWG max though; what the OP really needs is something like an Al9Cu insulated mechanical connector (Polaris(tm) or equivalent) Commented Mar 5, 2020 at 0:12
  • @ThreePhaseEel Thanks. Good catch!
    – HoneyDo
    Commented Mar 5, 2020 at 0:18