Have a row of ceiling lights which used to work about 10 years ago. Want to get an understanding of the wiring at the switch before I go to the effort of removing the ceiling panels which holds the fittings (not an easy job).

There are 4 lights which are connected to 2 switches, one upstairs and one downstairs. The idea was that you could switch the lights on at either switch.

The upstairs switch is standard, one wire in and one going out. Downstairs is wired as per below:

enter image description here

This is the houses original wiring, so the colours won't make much sense.

The switch in question is the top one. In the left connection is hot coming in. The top connection is typically for switched going out. The bottom connection is typically for loop. You can see both the top and bottom are a yellow wire.

Going into each light fixture is modern/standard Australian wiring with one wire for hot, one for neutral and one for earth. The earth is not connected into the fitting, but the hot and neutral are. The next length of wiring (going to the next light fitting), the hot and neutral are twisted into the incoming wiring, so they are also screwed into the connection with the incoming wiring.

My guess is that the downstairs switch has a loop and the upstairs one doesn't? Maybe the downstairs one has a loop with the first light.

2 Answers 2

1

Not a direct answer, but a way to clue you in if nobody else comes along with an answer:

I had to diagnose the wiring on my house when I first moved in. What I did, I first turned off the power on the circuit, then after being sure it was off, I connected a little 9V battery across two wires.

I had my wife stand at the other light switch, and with a multimeter (or voltmeter) check the wires to find which two I was holding in my hands. If you find +9V, the wire contacting the positive lead of the multimeter is the wire touching the positive side of the battery. If you find -9V, the wire contacting the positive lead of the multimeter is the wire touching the negative side of the battery.

If you identify all your wires, and what goes to where, you can make sense of it by drawing a diagram.

2
  • Thanks. Def something I could try, I have a multimeter and 9V battery.
    – going
    Feb 18, 2020 at 3:35
  • 1
    I would put about a 10k ohm resistor in series with that 9V battery. That way you don't instantly waste it if there's a short. Feb 18, 2020 at 8:36
1

First that wiring is very old it looks like Fabric-Insulated Electrical Wire which was used in the 50's and 60's and it really should be replaced as the insulation may not be protecting the wires which could be the reason the lights are not working.

The top switch your referring to is wired as a two way switch the middle wire will be the Common which, if it follows the modern way of wiring, will be connected to the light fixture and will either be the permanent live or the switched live. The other two wires will be the switch terminals 1 & 2 , I believe known in the US as the "traveler wires", and will be connected to the other switch upstairs.

One of the switches will have permanent live on the Common and the other will have a switched live.

https://www.dlsweb.rmit.edu.au/Toolbox/electrotech/toolbox1204/resources/04diagrams/04lighting/03_2way_sw.htm

1
  • Hello, and welcome to Home Improvement. Thanks for the answer; keep 'em coming. And, you should probably take our tour so you'll know the details of contributing here. Mar 25, 2020 at 12:08

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge that you have read and understand our privacy policy and code of conduct.

Not the answer you're looking for? Browse other questions tagged or ask your own question.