So I bought a house built in 1957. And all of a sudden after plugging a laptop into a bedroom on the other side of the house, all the overhead fixtures on the opposite side of the house stopped working.
So I went out and bought a new overhead took the old one down and was left with a mount which had a black wire and a white wire.
I figured it would be easy, I went out and bought a new fixture and hey! All I had was a black wire and a white wire. So I put them together and nothing happened.
I'll note that I used an electrical tester on both the switch which had roughly 110 going to it, turned it off tested the fixture had nothing going to it, turned it back on tested the fixture and there was the right amount of power there.
So I thought perhaps there was a ground wire I had missed or maybe the connections weren't tight or what have you and would I still couldn't get it to work.
But then accidentally I touched the white wire to the metal of the mount, one of the screws as a matter of fact and now it works perfectly.
This can't possibly be safe can it? The new fixture had a skinny copper ground while the old fixture had no ground wire coming from the ceiling nevertheless I hooked up the ground but with that hooked up it still didn't work.
So for my lite fixture to work I need to have black to black, white to metal mounting bracket and copper ground to wherever. Why is this happening? Is it going to burn my house down? What's the deal? Please and thank you
  • Can you post photos of the inside of the ceiling box please? Feb 17 '20 at 1:03
The fixture needs black to black, white to white and ground to the mount or electrical box. If this doesn't work, then you have an open neutral somewhere in the line and you need to find out where it is. You'll have to check everything on the circuit to determine where the open neutral is. Do not keep the white wire connected to the mounting bracket (which is probably grounded),because you're completing the circuit through the ground path, This is dangerous, it could kill you.
This is a very common blunder...
and I'm glad you caught yourself. The blunder is trying random things until something works, then declare enter image description here ... many of those combinations will work and then kill you.
This is certainly one of them.
Mains electrical has an "Equipment Safety Ground". The wires are always green, yellow-green, or bare. They should all be connected to each other and to nothing else. Their One Job is carrying fault current back to the panel so the breaker can trip. Back in the panel, the neutral wire has an equipotential bond to the ground rods, for the purpose of assuring the hot wires can't float thousands of volts above ground voltage, and for providing a fault current path.
Because of this, there is fairly good continuity between neutral and ground, which leads some to believe ground is a substitute for neutral. Not so at all. In fact, if you do that and your ground wire breaks or your ground rods have a problem, it can electrify every ground on the circuit or in the house. Suddenly what is supposed to be safe is dangerous.
Electricity is not supposed to be dangerous like that, and it won't be if you follow the electrical codes, which are law.
Don't fix 2 things at once
Your original problem is that several light fixtures went out. I imagine you do not know how to troubleshoot that. So you decided to "throw parts at it and hope for the best", so you created a project to replace one fixture. That had zero chance of fixing the problem, which, obviously, included four fixtures.
It's vanishingly unlikely that you would have 4 light fixtures fail at once. So there is clearly one single failure point that failed all of them, and possibly other stuff as well.
This is confirmed by the fact that you changed the fixture, and ... nothing changed.
The root problem is loss of neutral upline
Somewhere at one of the receptacles or switches, the neutral wire has developed a loose connection.
It's not too hard to find it if you know which circuit it is on. (since you can detect hot, you can turn off breakers until the hot goes away).
Once you know what circuit it's on, turn off all other circuits, and turn some loads "on" on the circuit. Check every outlet for a hot "hot" (meaning it is on this circuit) and a hot "neutral" (meaning it is on the far side of the neutral break).
The loss of neutral connection is either at the first dead outlet, or the last good one. It is probably a "backstab" connection that has gotten loose. If the screw terminal is cold but the backstab wire is hot, you found it!