I have a deep double fryer I am wiring up, voltage is 208/240, power is 5400/7200 watts, it will be 45 feet from the main electric panel, what size wire and fuses should I use
-
What sort of occupancy is this in? Is the wiring going to be exposed or concealed?– ThreePhaseEelFeb 16, 2020 at 21:38
-
What do the instructions call for?– JACKFeb 16, 2020 at 21:45
1 Answer
You'll need 8 AWG copper wire. Your breaker will need to be 40A and 2-pole. Unless the labeling or instructions says otherwise.
-
-
3Yes. 5400/208=26amp plus 25 percent equals 32amp therefore 40amp breaker. Feb 16, 2020 at 23:12