6

I have installed an EV level 2 charger in my garage. It is a 30 amp charger. It is around 8 feet away from the breaker box. I used 8/2 wire to be on the safe side for future possible upgrades and used a 2 pole 40 amp breaker, as required by the EVSE instructions.

The EV charger is working fine. The question I have is that the two hot wires are 8 gauge but the ground wire is a bare 10 gauge wire. Is this OK or should I replace the ground with an 8 gauge wire?

4
  • 2
    If the data plate on the charger calls for a 30A circuit, you should use a 30A breaker to protect it. Using bigger wire is fine, but the breaker needs to be sized for the "appliance" requirements.
    – JPhi1618
    Commented Feb 10, 2020 at 19:26
  • 3
    Does this answer your question? Why are ground wires required to be so large if a short results in an immediate breaker trip?, and this answer specifically has the NEC chart that lists the conductor sizes. You should be fine.
    – JPhi1618
    Commented Feb 10, 2020 at 19:33
  • JPhil1618 Thank you for your reply. The appliance requires a 40 amp breaker. My concern is with the ground wire being thinner than the 2 hot wires.
    – Ali
    Commented Feb 10, 2020 at 19:36
  • 2
    For "the next time" consider that it's usually easy to run conduit 8 feet, and if the device's terminals go to 75C (and your breakers do - mine do, certainly) you can carry more current on THHN in conduit than you can on "the same size wire" as a cable (limited to 60C rating.) In the case of 8 Ga copper, 50 rather than 40 A.
    – Ecnerwal
    Commented Feb 11, 2020 at 1:21

2 Answers 2

12

Yes, a 10 AWG ground wire is fine for up to a 60A circuit.

The 8/2 Romex (NM) cable is good for amperage up to 40 amps. However, the breaker must match the socket / EV charger spec. If the socket is a NEMA 6-30 or 14-30, the breaker must be 30A. If the EV charger docs specify 30A breaker, then that must be so.

Again, the 8/2 cable is perfectly fine for 30A or really any size up to 40A. So if your spec calls for a 30A breaker, you only need to change the breaker. 30A sockets will accept #8 wire.

It is possible that a 30A-nameplate charger might want a 40A breaker. The documentation will tell the tale.

3
  • Thank you so much for your help. So to make sure I have a good enough understanding of this thing, the ground wire is actually not in constant use and it is only there in case of a short or malfunction, that's why it does not need to be as thick as the 2 hot wires, right?
    – Ali
    Commented Feb 10, 2020 at 19:48
  • @Ali Correct. Flow on equipment safety ground only occurs during fault conditions. Commented Feb 10, 2020 at 20:15
  • Thank you so much for your kind help. You guys are AWESOME.
    – Ali
    Commented Feb 10, 2020 at 20:20
-1

#10 then is only good for 30 amps , correct this before too many people see this

As requested, correcting this: using the chart from https://diy.stackexchange.com/a/151175/18078

enter image description here

2

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.